Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread William Miller
-boun...@lists.re-wrenches.org] *On Behalf Of *Rebekah Hren *Sent:* Tuesday, July 20, 2021 6:20 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Snap-n-rack bonding certification Minor update, I got word from Snapnrack that: "The new protocol established with UL eliminates the need to includ

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread jay
Can WEEBS be used instead? jay peltz power > On Jul 20, 2021, at 4:37 PM, Rebekah Hren wrote: > > Hi William > > Groan, I don't see that precise model in the series 100 installation manual > > on pg 7

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Rebekah Hren
Minor update, I got word from Snapnrack that: "The new protocol established with UL eliminates the need to include the wattage ranges for each module type" Still a pain and the manufacturer/model should be on the rack manufacturer list - but not down to the precise wattage - so slightly less of a

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Rebekah Hren
Hi William Groan, I don't see that precise model in the series 100 installation manual on pg 74 which is the bonding evaluation list of modules I hope for your sake Snapnrack will send an email the AHJ will acce

Re: [RE-wrenches] Snap-n-rack bonding certification

2021-07-20 Thread Sam Haraldson
The SnapNrack UL 2703 document highlights it's UL listing when used with Type 1 and Type 2 modules. https://snapnrack.com/wp-content/uploads/2019/05/SnapNrack_Fire_Classification_Tech_Bulletin_v.2-1.pdf *SnapNrack Series 100, Ultra Rail and RL systems have been Certified for a Class A fire rating