You said that very nicely Kevin !
If this were for offgrid, I would make the inspector happy and do even
more than Kevin suggests after he is gone. 😉
Link to RS shutdown
https://www.youtube.com/watch?v=wMoVXq4m1wk&t=10s
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://
Hi Mac,
I’ve just gone through a couple installations with a similar situation.
The hardware you list does work as intended. I had to go through three
different suppliers to get all the components.
One thing that I didn’t find clear in the MPPT RS documentation is when a
shutdown is initiated,
Note that the MPPT disco RS works only with Schneider charge controllers.
With any other charge controllers you'll need to use Fire Raptors.
Specifically the power line type rsd do not work with classic cc. I see no
reason why the Schneider units would not meet 2020 or 2023 codes.
On Mon, Jan 1,
I had a some way similar experience I used fire raptor and added a relay to
use Raptor signal to shutdown inverter.
On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hello Wrenches,
>
> I need to retrofit a Schneider XW+ system with a rapid shutd