Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-02 Thread Dave Angelini Offgrid Solar via RE-wrenches
You said that very nicely Kevin ! If this were for offgrid, I would make the inspector happy and do even more than Kevin suggests after he is gone. 😉 Link to RS shutdown https://www.youtube.com/watch?v=wMoVXq4m1wk&t=10s Dave Angelini Offgrid Solar "we go where powerlines don't" [1]https://

Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-02 Thread Kevin Pegg via RE-wrenches
Hi Mac, I’ve just gone through a couple installations with a similar situation. The hardware you list does work as intended. I had to go through three different suppliers to get all the components. One thing that I didn’t find clear in the MPPT RS documentation is when a shutdown is initiated,

Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-01 Thread Bradley Bassett via RE-wrenches
Note that the MPPT disco RS works only with Schneider charge controllers. With any other charge controllers you'll need to use Fire Raptors. Specifically the power line type rsd do not work with classic cc. I see no reason why the Schneider units would not meet 2020 or 2023 codes. On Mon, Jan 1,

Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-01 Thread Darryl Thayer via RE-wrenches
I had a some way similar experience I used fire raptor and added a relay to use Raptor signal to shutdown inverter. On Mon, Jan 1, 2024, 2:01 PM Mac Lewis via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hello Wrenches, > > I need to retrofit a Schneider XW+ system with a rapid shutd