Yes it can be done, I was testing the sma1800 years ago with an outback 24
volt inverter and it worked fine with in its power range.
On Fri, Sep 20, 2019, 6:41 AM Dave Tedeyan wrote:
> Hi all,
>
> I get asked this question frequently, as I am sure many others do, and of
> course the first answe
manently
delete the original and any copies of this email and any attachments thereto.
Thank you.
From: RE-wrenches On Behalf Of Dave
Tedeyan
Sent: Friday, September 20, 2019 8:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Running a grid tied system when the grid is down
Hi Brad,
Not a bad idea wi
tember 20, 2019 9:07 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Running a grid tied system when the grid is down
Hi Mike,
For rapid shutdown, we are on NEC2014 in NY. So module level is not necessary.
And the SPS is a huge reason for the SB inverters on this one. And in this
case, it is almost exac
The downside of the SMA SPS is there is very little headroom to surge
and start a well pump or a fire pump. There is also the major problem of
sundown.
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 81
Hi Mike,
For rapid shutdown, we are on NEC2014 in NY. So module level is not
necessary.
And the SPS is a huge reason for the SB inverters on this one. And in this
case, it is almost exactly what the homeowner is looking for. But with the
two inverters, can those SPS be wired into a panel rather th
Dave – how is Rapid Shutdown being complied with? And what load requires 240V
– or is that needed to “fool” the PV inverters?
With two SB-40s, you have the ability to wire for the homeowner two Secure
Power Supply circuits – and get up to 2000W (at 120VAC) from each when sun is
up and grid is
Hi Brad,
Not a bad idea with this one to run the loads off the SPS's. Has anyone
ever tried wiring these directly into a panel, rather than into an outlet?
And do you know if the 120V signal from each one would match up, or do they
work independantly? In other words can you wire both SPS into the s
If you're not using the SB -40 inverter's rapid shutdown system, it has the
SPS Secure Power Supply which does just what your customer wants.
My understanding from talking to inverter mfg, is that trying to do AC
coupling with a smaller battery inverters does not work because the
anti-islanding in