renches.org] On Behalf Of August Goers
Sent: Wednesday, October 09, 2013 3:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Point of connection question
William,
You have 9 M190s each running at 800 mA according to spec sheet. That equals
7.2 A nominal output current. Plus you have 10 M250s
William,
You have 9 M190s each running at 800 mA according to spec sheet. That
equals 7.2 A nominal output current. Plus you have 10 M250s (if you look at
your drawing) each running at 1 A = 10 A. 7.2 A + 10 A = 17.2 A * 1.25 =
21.5 A min breaker size. So, you'll need to round your breaker to a
HI William;
I think you might have a problem. Looking at Enphase's ratings, the
M190 has an output rating of 800mA, while the M250 has an output rating
of 1.0 A. 10 M250s = 10 amps, 9 M190s = 7.2 amps
17.2 amps exceeds 80% of your 20 amp breaker.
I know this won't actually happen, but my und