Re: [RE-wrenches] Looking for remote controlled contactors

2022-10-12 Thread Jason Szumlanski via RE-wrenches
Ask any HVAC tech how many 240V contractors they replaced this week alone on condenser units. They carry boxES on their trucks around here. Granted, those are engaged far more frequently than in a PV system application, enduring many cycles per day. But it's still not a failsafe solution. In my op

Re: [RE-wrenches] Looking for remote controlled contactors

2022-10-12 Thread Drake Chamberlin via RE-wrenches
I haven't had problems with contactors failing. I suspect that a lot of the problems on battery systems happen when contactors are controlled at battery voltage. The nominal voltage of the system is not what the coil will see. A 48 VDC coil might experience 63 VDC. A resistor needs to be put in

Re: [RE-wrenches] Looking for remote controlled contactors

2022-10-12 Thread Kirk Herander via RE-wrenches
You are correct on this. The failure of any control hardware, IO's / relays / contactor logic along the way from generator sense to PV contactor should result in the coupled grid-tie PV inverter disconnected. Which means the contactor at the PV inverter should be energized "closed" (so PV AC conne

Re: [RE-wrenches] Looking for remote controlled contactors

2022-10-11 Thread Jason Szumlanski via RE-wrenches
I'm not a fan of this strategy because it is not failsafe. Contactors fail. When the coil fails to open the contactor, you will have the PV AC coupled with the generator If he normally closed contactor is used in this manner. I think the question needs to be the converse: How do you turn the PV on

Re: [RE-wrenches] Looking for remote controlled contactors

2022-10-11 Thread Maverick Brown via RE-wrenches
I’ll usually use a 60 amp contactor with 240Vac coil. The generator powers the coil and opens the Normally Closed contacts disconnecting the grid tie inverter. Maverick Brown Off-Grid Solar Commander since 2006 Maverick Solar Enterprises, Inc. • Solar Commander Remote Power • SunFlow System