Re: [RE-wrenches] Generator brains

2015-07-16 Thread Jarmo . Venalainen
Hi: Having both connected will work the way you want, only if you make sure the solar charger charging voltage is higher than the Kohler charger voltage. When the solar charging source has higher voltage it will trump the lower Kohler charging voltage an do the charging when the sun is out. W

Re: [RE-wrenches] Generator brains

2015-07-16 Thread Will White
n Sindelar Sent: Thursday, July 16, 2015 1:54 PM To: RE-wrenches Subject: Re: [RE-wrenches] Generator brains Bill, This is the new reality, for better or worse. Most gennies are primarily built for residential backup and use the grid AC to maintain readiness. In a new installation, runnin

Re: [RE-wrenches] Generator brains

2015-07-16 Thread Allan Sindelar
(Accidentally hit send before finished) A few years ago we addressed this on a Kohler 11RES installation. We put a 20w module and controller on the starting battery for the control load. The other loads - carb heater and something else I don't recall - ran off the inverter's AC, but with a manu

Re: [RE-wrenches] Generator brains

2015-07-16 Thread Allan Sindelar
Bill, This is the new reality, for better or worse. Most gennies are primarily built for residential backup and use the grid AC to maintain readiness. In a new installation, running one more conductor to carry system AC for the generator, often no larger than 14awg, with the output and signal b

Re: [RE-wrenches] Generator brains

2015-07-16 Thread Tump
Using a Atksen Gen wizard will allow the installer to have a; start on low starter battery voltage as well as start on low temp feature. If its a propane unit I always use the carb heater 1) helps the unit start &20 cycles the unit more often in the winter due to the load of the carb heater. OR