Propane generator expert here - certified Generac technician.
Chances are the problem lies with the fuel supply. Your inverter is working
better, taking more power, putting more current into the batteries.
Therefore the generator, which is well within it's rating, is taking more
fuel.
99% of propa
4G LTE smartphone
Original message
From: Mike Kocsmiersky
Date: 4/26/2016 12:41 AM (GMT-10:00)
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Battery charging problems
Chris,
In theory the upgraded batteries should be able to accept a greater current
(or at least
Chris,
In theory the upgraded batteries should be able to accept a greater current
(or at least max charge current) for a greater length of time than the prior
battery bank. I once had a propane genset run rough when it was starved for
fuel, due to an undersized upright propane cylinder which coul
That doesn't make sense, the inverter's charger determines the max
charge rate and the max draw from the generator.
The 8.5 kW Kohler should have no problem running the 4.4 kW Magnum.
What is the altitude?
Is it wired for 240 vac ? If the generator is running at 120 vac, then
you are only r
Hi Chris,
The problem summary is a bit light on details to be too specific. What,
precisely, does a generator running "rough" mean? Overheating? Smoking? Breaker
tripping?
THE MS4448 has about 3 kW charging capability (63A @ 50 VDC). So the 8.5 kW
Kohler should be able to handle that easily,