Re: [RE-wrenches] Apparent power

2012-02-07 Thread Comet Systems
Interesting but way smaller scale than I was thinking. The Anguilla grid has a capacity of 10 - 15MW from a single diesel generating station. 2012/2/7 Richard L Ratico > Chris, > > Perhaps you'll find this island's experience of interest: > > http://www.isleofeigg.org/eigg_electric.html > > Dick

Re: [RE-wrenches] Apparent power

2012-02-07 Thread Richard L Ratico
Chris, Perhaps you'll find this island's experience of interest: http://www.isleofeigg.org/eigg_electric.html Dick Ratico Solarwind Electric --- You wrote: Ray, The idea that the utility in an island is seeing an advantage to having PV on the grid is a huge concept for me. As I am based in a

Re: [RE-wrenches] Apparent power

2012-02-06 Thread Darryl Thayer
think inverters can reactive correction, why not use a capacitive device?   Darryl From: "b...@midnitesolar.com" To: RE-wrenches Sent: Saturday, February 4, 2012 8:05 PM Subject: Re: [RE-wrenches] Apparent power Sounds like a voltage source (a

Re: [RE-wrenches] Apparent power

2012-02-06 Thread Ray Walters
Hi Chris; Marco Manglesdorf (on this list) is the man to talk to about that. He is based in the Hawaiian islands; I only had the good fortune to work for him for a few projects. Ray Walters On 2/6/2012 5:30 PM, Comet Systems wrote: Ray, The idea that the utility in an island is seeing an a

Re: [RE-wrenches] Apparent power

2012-02-06 Thread Comet Systems
Ray, The idea that the utility in an island is seeing an advantage to having PV on the grid is a huge concept for me. As I am based in a small island with a utility that is scared of solar pv installations, this concept is tremendous ammunition for me. I am also fascinated by the idea of PV insta

Re: [RE-wrenches] Apparent power

2012-02-05 Thread Ray Walters
I was just wondering about this same issue: of inverters being used to support the grid. Just as charge controllers reduce their output current as the voltage reaches absorption voltage, I was thinking that GT inverters could do the same thing, instead of just shutting off, and not reconnectin

Re: [RE-wrenches] Apparent power

2012-02-04 Thread b...@midnitesolar.com
Sounds like a voltage source (and sinking) inverter to me. These types can cause current distortion which the UL1741 / IEEE 1547 specs try to prevent. Apparent must be able to turn that mode on and off I would imagine. It's not too difficult to do. No wonder they talk about micro-grids.

Re: [RE-wrenches] Apparent power

2012-02-04 Thread Comet Systems
As I understand the issue they claim to be able to address, the utilities often need a source of reactive power close at the system delivery points, the customer sites, because reactive power does not transmit well through the lines and transformers and uses up transmission resources better used fo

Re: [RE-wrenches] Apparent power

2012-02-04 Thread Bill Hoffer
Keith I was involved with doing some testing with these guys for a company that wanted to manufacture them in Washington State ( made in WA incentives) and the concept is good, but I had a lot of questions that they were not able to answer. Big one is the inverter was producing 10watts all night