Re: [RE-wrenches] 3-phase with storage

2018-05-18 Thread Jamie Rennie
Solaredge offers a three-phase battery system option using one of their inverters with LG Chem batteries on one leg. On Tue, Apr 17, 2018 at 4:35 PM, Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > The 2 Lithium batteries I use are HALT tested but it is always a big risk > with a bat

Re: [RE-wrenches] 3-phase with storage

2018-04-18 Thread Dave Angelini Offgrid Solar
The 2 Lithium batteries I use are HALT tested but it is always a big risk with a battery that may out live many of the clients. The math on these batteries has them lasting 30 to 40 years offgrid and that is pretty hard to believe! Will the BMS fail or the battery? If they can afford it I have the

Re: [RE-wrenches] 3-phase with storage

2018-04-17 Thread Darryl Thayer
I have done it, not hard but limited to 32 kw for backup power, 120/208 3 phaze using Outback FXR On Tue, Apr 17, 2018, 1:19 PM Marco Mangelsdorf wrote: > Aloha all. > > I'm on the hunt for workable options for a PV plus storage design for a > 3-phase 120/208 application. > > And there ain't muc

Re: [RE-wrenches] 3-phase with storage

2018-04-17 Thread Kevin Pegg
We are building a similar system presently, 60 kW Sunny Island Inverters, 400 kWh battery storage (FLA), dual 100 kW backup generators, 25 kW PV, 5 kW microhydro. Don't know what raw capacity you are looking for, we also use XW inverters for smaller systems but find they don't scale nearly as w

Re: [RE-wrenches] 3-phase with storage

2018-04-17 Thread Dave Angelini Offgrid Solar
I do not want to sound like I am plugging Discover AES batteries and there use with Schneider and soon Outback. There web page has a 3 phase XW+ system on it and all the coms built in to the BMS to work with Xanbus. AEE had a webinar also last week. It is on their U-tube channel. Dave Angelini Off

Re: [RE-wrenches] 3-phase with storage

2018-04-17 Thread Jerry Shafer
Marco Outback R is available we got batteries too, we ccn talk off list if you like, im on island too Jerry On Tue, Apr 17, 2018, 8:19 AM Marco Mangelsdorf wrote: > Aloha all. > > I'm on the hunt for workable options for a PV plus storage design for a > 3-phase 120/208 application. > > And there

Re: [RE-wrenches] 3-phase with storage

2018-04-17 Thread Will White
SMA Sunny Island, Outback, and Schneider can all be configured for three phase systems. On Tue, Apr 17, 2018 at 1:47 PM, Marco Mangelsdorf wrote: > Aloha all. > > I'm on the hunt for workable options for a PV plus storage design for a > 3-phase 120/208 application. > > And there ain't much out t