Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Marco Mangelsdorf
-boun...@lists.re-wrenches.org] On Behalf Of Howard Arey Sent: Monday, June 13, 2016 11:11 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] 20 kW 208/120 inverters Consider using three single phase inverters putting out 208; one inverter for AB leg, AC leg, and BC leg. Howard “

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Glenn Burt
d 6kW. -Original Message- From: "Howard Arey" Sent: ‎6/‎13/‎2016 14:11 To: "'RE-wrenches'" Subject: Re: [RE-wrenches] 20 kW 208/120 inverters Consider using three single phase inverters putting out 208; one inverter for AB leg, AC leg, and BC leg. Howar

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Peter Parrish
. Suite 351 South Pasadena, CA 91030 (323) 839-6108 peter...@pobox.com From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Howard Arey Sent: Monday, June 13, 2016 11:11 AM To: 'RE-wrenches' Subject: Re: [RE-wrenches] 20 kW 208/120 inverters Cons

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Carl Adams
Jason, Howard, I could certainly use multiple smaller inverters. I was just looking to see if there was a larger 208 inverter available. Seems the upper limit on the 208Y/120V inerters is at about 14kW. One larger inverter is almost always less expensive than two smaller ones in terms of initia

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Jason Szumlanski
You're right. They share the same installation an user manuals, so I assumed they were the same output voltage. Is there a reason you can't use a pair of 10kWs? On Mon, Jun 13, 2016 at 4:09 PM, Carl Adams wrote: > Jason, > > It looks like the 14k is 208/120V but the 20TL is 277/480 > > Carl A

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Carl Adams
Jason, It looks like the 14k is 208/120V but the 20TL is 277/480 Carl Adams SunRock Solar NABCEP Certified PV Installer On Mon, Jun 13, 2016 at 2:15 PM, Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > Solectria PVI 20TL would meet your criteria. I can't vouch for it > personally,

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Howard Arey
Consider using three single phase inverters putting out 208; one inverter for AB leg, AC leg, and BC leg. Howard “Scot” Arey 254-300-1228 scot.a...@solarcentex.com From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Be

Re: [RE-wrenches] 20 kW 208/120 inverters

2016-06-13 Thread Jason Szumlanski
Solectria PVI 20TL would meet your criteria. I can't vouch for it personally, but I've seen quite a few 14TL successfully installed in commercial applications. On Mon, Jun 13, 2016 at 2:08 PM, Carl Adams wrote: > Hello Wrenches, > > I am looking of a recommendation on a 208 3 phase inverter i