From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard L
Ratico
Sent: Tuesday, August 31, 2010 4:45 AM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] phase issues with SB8000US
Hi Nik,
Some questions:
Is this a
the other leg. Perhaps the
SB is causing both legs to drop. Ask SB if it is OK to disconnect the neutral,
keep the ground.
Darryl
--- On Tue, 8/31/10, Richard L Ratico wrote:
> From: Richard L Ratico
> Subject: Re: [RE-wrenches] phase issues with SB8000US
> To: re-wrenches@lists.re-
Hi Nik,
Some questions:
Is this a 3 phase service?
Details on the UPS; brand, kVA, age?
Breaker sizes for the circuit(s) supplying the UPS and fan?
Details on the air conditioning system and fan. Are they powered through the
UPS?
Dick Ratico
Solarwind Electric
--- You wrote:
Wrenchers,
We i
Wrenchers,
We installed our first SunnyBoy 8000 this month. The customer (happens to be
electrical engineer) is complaining that their computer UPS systems are
tripping whenever the air conditioner (with 120V fan) comes on. This didn't
happen before commissioning the solar system and it doesn't ha