Re: [RE-wrenches] outdoor disconnects on multiple buildings

2010-11-22 Thread Dave Click
I think that if you have the 705.10 directory showing the disconnect locations (a directory at each location), you'd be OK per NEC. I think this question is likely one to ask your utility- the language may be in your interconnection agreement and you likely already know how flexible utilities a

Re: [RE-wrenches] outdoor disconnects on multiple buildings

2010-11-22 Thread dan
o concur (again, unless I'm seriously missing something)... I dunno...  I think you're good... would be interesting to find out.. Waiting for the eggs to fly.. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Mes

Re: [RE-wrenches] outdoor disconnects on multiple buildings

2010-11-21 Thread Richard L Ratico
Hi Kirk, See 2008 NEC 225.30 thru 225.40. As I understand it, separate disconnects, up to six for each array, located on the main building, are required and appropriate. Dick Ratico Solarwind Electric --- You wrote: Hello, I'm working on a system which will have 5 kw on an outbuilding and 20k

[RE-wrenches] outdoor disconnects on multiple buildings

2010-11-20 Thread Kirk Herander, VSE
Hello, I'm working on a system which will have 5 kw on an outbuilding and 20kw on the main building, all Enphase inverters, I plan to put an AC disco for the 5kw on the outside of its building and another on the outside of the main building for the 20 kw array. Both arrays feed into the main pa