I think that if you have the 705.10 directory showing the disconnect
locations (a directory at each location), you'd be OK per NEC. I think
this question is likely one to ask your utility- the language may be in
your interconnection agreement and you likely already know how flexible
utilities a
o concur (again, unless I'm seriously missing something)... I dunno... I think you're good... would be interesting to find out.. Waiting for the eggs to fly.. dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44
Original Mes
Hi Kirk,
See 2008 NEC 225.30 thru 225.40. As I understand it, separate disconnects,
up to six for each array, located on the main building, are required and
appropriate.
Dick Ratico
Solarwind Electric
--- You wrote:
Hello,
I'm working on a system which will have 5 kw on an outbuilding and 20k
Hello,
I'm working on a system which will have 5 kw on an outbuilding and 20kw on
the main building, all Enphase inverters, I plan to put an AC disco for the
5kw on the outside of its building and another on the outside of the main
building for the 20 kw array. Both arrays feed into the main pa