2010-09-07 Thread Kent Osterberg
Matt, I agree with you on about 98% of this.  You are 200% correct that a faulted high-voltage or high-current PV array is a serious and dangerous situation and that the person looking for the trouble in a faulted PV array needs the proper tools and knowledge of how all the components work.  B

Re: [RE-wrenches] ground fault troubleshooting

2010-09-06 Thread William Miller
Colleagues: I have been saying for some time that we need to rethink PV ground fault indicator systems. The fundamentals of existing GFI systems is for the bond between the grounded-conductor and the grounding-conductor to be opened upon a ground fault. This bond is important for safety and

Re: [RE-wrenches] ground fault troubleshooting

2010-09-06 Thread Matt Lafferty
e arcing when you land/un-land the jumper &/or remove the fault. If the sun is shining and you have a DC fault, you will have arcing at some point when you make/break the circuit. Hopefully it's safely contained and localized to the contacts of a service disconnect! Pray for Sun! Matt Lafferty

Re: [RE-wrenches] ground fault troubleshooting

2010-04-05 Thread Bill Brooks
: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Tom DeBates Sent: Monday, April 05, 2010 7:04 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] ground fault troubleshooting hello Wrenches, We recently had an interesting

[RE-wrenches] ground fault troubleshooting

2010-04-05 Thread Tom DeBates
hello Wrenches,   We recently had an interesting (amusing?) experience that I thought might be worth sharing and to get some feedback.   I received a call from a fellow contractor that had a ground fault in his PV system (Wattsun DA tracker, 24 Siemens (Shell?)110, 1 string, Sunny Boy 2500). The