Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-14 Thread Jarmo . Venalainen
/2014 02:36 PM Subject: Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting) Sent by: "RE-wrenches" Drake, No, and unless and until it comes up again, they won't. My drama with them in January led to a draw: I put in a vent fan and they tabled the issue without broade

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-03 Thread Allan Sindelar
Drake, No, and unless and until it comes up again, they won't. My drama with them in January led to a draw: I put in a vent fan and they tabled the issue without broader resolution and approved the final inspection so the clients could move in.

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-03 Thread Allan Sindelar
14 12:08 PM To: RE-wrenches Subject: Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)   Allan, That was my plan when he insisted on venting to the outside. I

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread RE Ellison
4 12:08 PM To: RE-wrenches Subject: Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting) Allan, That was my plan when he insisted on venting to the outside. I use the Zephyr Power Vent for liquid lead acid batteries. When replaced the liquid electrolyte batteries in our backup s

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread Drake
Allan, That was my plan when he insisted on venting to the outside. I use the Zephyr Power Vent for liquid lead acid batteries. When replaced the liquid electrolyte batteries in our backup system with AGM, we turned off the Zephyr and took the door off the battery box. I showed it to the clie

Re: [RE-wrenches] Battery Venting (WAS Passive Battery Venting)

2014-11-02 Thread Allan Sindelar
Drake, My suggestion is that to achieve the client's wishes as well as your own cooling concerns, you include a Zephyr Power Vent in a 2" PVC vent stack to the outside. Let the charge controller's voltage-actuated auxiliary setting power the vent (it's OK to do

Re: [RE-wrenches] Battery venting issue

2014-02-06 Thread Larry Crutcher, Starlight Solar Power Systems
Allan, The primary concern should be the volume of gas discharge if over voltage occurs. This study helped me understand the risks: http://www.sonnenschein.org/Gassing.htm Quote from the study: "Gassing according to IEC 896/2-Oct 95 @ 2.3v / cell within 30 days was measured @ 5mL/cell/ah while

Re: [RE-wrenches] Battery venting issue

2014-02-05 Thread Phil Undercuffler
Allan, The International Fire Code (2006 version quoted below, confirm the version used in your region) give us clear guidance on the ventilation requirements for stationary battery systems, and provides both engineering parameters and prescriptive solutions clearly spelled out . These can be us

Re: [RE-wrenches] Battery venting issue

2014-02-05 Thread Ray Walters
I can give you one example for them to consider: UPS systems. They all use sealed VRLA batteries, and are not vented to the outside. 2nd thing for them to chew on: The Midnite Battery boxes are ETL listed, and you are installing them to the manufacturer's recommendations. 3rd, your use of arti

[RE-wrenches] Battery venting issue

2014-02-05 Thread Allan Sindelar
Wrenches, I need a bit of help here if you have it. Since 2002 we have installed somewhere between 30 and 35 systems with sealed batteries installed in manufactured enclosures, originally Outback enclosures and in recent years Midnite MNBE enclosures. At least ten of thes

Re: [RE-wrenches] battery venting; Corrosion

2012-01-16 Thread Ray Walters
I've found the Zephyr Power vents to be a little undersized in larger batteries with arrays over 1000 watts. Still get that smell in the room outside of the battery box, though its not explosive. That was with the 12 v model. I wouldn't mind seeing someone make a similar vent plumbed to larg

Re: [RE-wrenches] battery venting; Corrosion

2012-01-16 Thread Kent Osterberg
John, Thanks for the follow-up on this subject. I'd like to change the example to show the ventilation required rather than the hydrogen liberated. Consider a 48-volt bank of L16RE-B batteries: that's 24 cells of 370 amphours. Using the 14 cc/hr/Ah/cell H2 rate for equalizing gives a total h

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread John DeBoever
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Crutcher, Starlight Solar Power Systems Sent: Friday, January 06, 2012 6:20 PM To: RE-wrenches Subject: Re: [RE-wrenches] battery venting; Corrosion Hi John, I am curious about what you saying "float or equalization&qu

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread Larry Crutcher, Starlight Solar Power Systems
Correction: I meant to say .05*C20 for AGM equalization current. Larry On Jan 6, 2012, at 4:48 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Hello William, My understanding is once the SO4 is fully absorbed, excess H and O are produced and could be vented if the pressure rises abov

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread Larry Crutcher, Starlight Solar Power Systems
Hello William, My understanding is once the SO4 is fully absorbed, excess H and O are produced and could be vented if the pressure rises above 5psi. So, when saturation is complete, voltage should be reduced and no gassing would take place. For this reason, I always recommend using charge curre

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread Larry Crutcher, Starlight Solar Power Systems
Hi John, I am curious about what you saying "float or equalization". Here's my understanding: If the battery is able to accept all current presented, the electrochemical process, SO4 combining with H released through decomposition, is balanced and with little excess gas released. When the elect

Re: [RE-wrenches] battery venting re VRLA

2012-01-06 Thread Allan Sindelar
In reference to William's comment about equalizing VRLA batteries, see page 17 of Concorde Battery's SunXtender technical manual, available online at http://www.sunxtender.com/pdfs/Sun_Xtender_Battery_Technical_Manual.pdf. They instruct charging these AGM VRLA batteries

Re: [RE-wrenches] battery venting

2012-01-06 Thread Kent Osterberg
Wrenches, While looking for information regarding standards about battery room ventilation I ran into this link, which has some good information and is certainly worth everyone's attention. http://www.belvoir.army.mil/safety/inc/battery-explosion.asp Kent Osterberg Blue Mountain Solar, Inc.

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread William Miller
Larry: I always thought that any breach of a valve in a VRLA battery was a sign of a failure. I recently spoke with a technician at MK Batteries and learned that venting and/or seepage is not uncommon and not a sign of failure. I have also heard in the distant past and then read recently on

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread Larry Crutcher, Starlight Solar Power Systems
-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of bob ellison > Sent: Thursday, January 05, 2012 12:18 PM > To: 'RE-wrenches' > Subject: Re: [RE-wrenches] battery venting; Corrosion > > I have had great luck by heating Vas

Re: [RE-wrenches] battery venting; Corrosion

2012-01-06 Thread John DeBoever
m: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg Sent: Thursday, January 05, 2012 7:59 PM To: RE-wrenches Subject: Re: [RE-wrenches] battery venting; Corrosion John, Could you clarify units? "0.418 Liters/AH" is

Re: [RE-wrenches] battery venting; Corrosion

2012-01-05 Thread Kent Osterberg
un...@lists.re-wrenches.org] On Behalf Of bob ellison Sent: Thursday, January 05, 2012 12:18 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] battery venting; Corrosion   I have had great luck by heating Vaseline to the hot liqui

Re: [RE-wrenches] battery venting; Corrosion

2012-01-05 Thread bob ellison
January 05, 2012 10:37 AM To: RE-wrenches Subject: Re: [RE-wrenches] battery venting; Corrosion Almost all RV's have a small, poorly vented battery box with 4 GC2 batteries. We see corrosion all the time. When we replace batteries, we use zinc coated copper terminals and apply a thin layer o

Re: [RE-wrenches] battery venting; Corrosion

2012-01-05 Thread Larry Crutcher, Starlight Solar Power Systems
Almost all RV's have a small, poorly vented battery box with 4 GC2 batteries. We see corrosion all the time. When we replace batteries, we use zinc coated copper terminals and apply a thin layer of grease with a toothbrush to every exposed portion of the connectors. This simple step, with the oc

Re: [RE-wrenches] battery venting

2012-01-04 Thread dan
I concur. thank you.dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 Original Message Subject: Re: [RE-wrenches] battery venting From: "Jeff Yago" <jry...@dtisolar.com> Date: Wed, January 04, 2012

Re: [RE-wrenches] battery venting

2012-01-04 Thread Jeff Yago
Here is another issue related to this thread. Yes, you can build sealed battery boxes and add vent pipes, fans, whatever, but battery terminals and battery cables installed in a confined box will have far more problems with terminal corrosion due to more concentrated forms of gasses and a mist o

Re: [RE-wrenches] battery venting

2012-01-04 Thread Jeff Yago
Jay, I have had a solar charged 12v RV/marine battery explode inside a very large work trailer, but found that the battery was bone dry which may have been the real reason for the melt down and not a trailer full of gas as the only damage was a totally exploded battery case. I was working inside

Re: [RE-wrenches] battery venting

2012-01-04 Thread Larry Crutcher, Starlight Solar Power Systems
Hi Jay, I have. 4 golf cart batteries were installed in a non vented compartment of an RV...with other electronics like inverter, relays, solenoids, etc. I was about 500 feet away and heard an expolsion. When I arrived at the RV, the bay door was mostly blown off the hinges. Needless to say the

Re: [RE-wrenches] battery venting

2012-01-04 Thread Tom Duffy
...@lists.re-wrenches.org] On Behalf Of jay peltz Sent: Tuesday, January 03, 2012 4:05 PM To: RE-wrenches Subject: Re: [RE-wrenches] battery venting Hi All, We've been having this discussion about battery box explosions. I would like a show of hands who has actually seen or truly known of a ba

Re: [RE-wrenches] battery venting

2012-01-03 Thread William Dorsett
-wrenches Subject: Re: [RE-wrenches] battery venting H2 is actually very difficult to contain, and can migrate through most materials. A super sealed, very small space, with a lot of charging source, its possible to reach combustion, but IMHO, you'd have to really try to create a system to do

Re: [RE-wrenches] battery venting

2012-01-03 Thread Ray Walters
H2 is actually very difficult to contain, and can migrate through most materials. A super sealed, very small space, with a lot of charging source, its possible to reach combustion, but IMHO, you'd have to really try to create a system to do that. I've had a cell burn off its H2 once, so yes yo

Re: [RE-wrenches] battery venting

2012-01-03 Thread jay peltz
Hi All, We've been having this discussion about battery box explosions. I would like a show of hands who has actually seen or truly known of a battery enclosure that has exploded due to hydrogen gas build up. And some specifics about that occurrence if possible. Thanks, Jay peltz power

Re: [RE-wrenches] battery venting

2012-01-03 Thread Jeff Yago
Jeffrey, We installed many battery banks in basements for both backup and off-grid systems and in the past few years we have gone to battery “rooms” that were designed for this type use. These rooms include fire-rated interior drywall construction, an exterior window, a low intake vent louv

Re: [RE-wrenches] battery venting

2012-01-02 Thread William Dorsett
:47 PM To: RE-wrenches Subject: [RE-wrenches] battery venting I am doing this project in India. The cost structures here are a great deal more constrained that what we're used to. Using AGM batteries is going to be a deal-breaker with the client as far as cost. I also don't kno

Re: [RE-wrenches] battery venting

2012-01-01 Thread bob ellison
de of the box. Happy New Year, Bob Ellison Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Richard L Ratico Sent: Saturday, December 31, 2011 2:47 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] ba

Re: [RE-wrenches] battery venting

2012-01-01 Thread bob ellison
-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of JRQ Sent: Saturday, December 31, 2011 1:47 PM To: RE-wrenches Subject: [RE-wrenches] battery venting I am doing this project in India. The cost structures here are a great deal more

Re: [RE-wrenches] battery venting

2012-01-01 Thread dan
not. Let's be rational. Flammable Vapor is Flammable Vapor. and Explosive condition is an Explosive condition.I'm gonna go play.. . Happy new year everybody. the Sun returns dbDan BrownFoxfire Energy Corp.Renewable Energy Systems(802)-483-2564www.Foxfire-Energy.comNABCEP #092907-44 --

[RE-wrenches] battery venting

2011-12-31 Thread JRQ
rtified PV Installer Peripatetic Solar Technician From: bob ellison To: 'RE-wrenches' Sent: Sunday, January 1, 2012 5:06 AM Subject: Re: [RE-wrenches] battery venting Mount a BRUSHLESS fan inside the box blowing out into the pipe, do not pressurize the

Re: [RE-wrenches] battery venting

2011-12-31 Thread bob ellison
nches Subject: Re: [RE-wrenches] battery venting Hello Jeffrey, Since you're working under constrained conditions for the install, and apparently have little option on using the flooded/vented batteries, here are some suggestions that may help: 1) Do your best to ensure the battery enclosure is

Re: [RE-wrenches] battery venting

2011-12-31 Thread Exeltech
--- On Sat, 12/31/11, Michael Welch wrote: > From: Michael Welch > Subject: Re: [RE-wrenches] battery venting > To: "RE-wrenches" > Date: Saturday, December 31, 2011, 5:20 PM > > Exeltech wrote at 02:16 PM 12/31/2011: > > >4) Install the vent fan on the

Re: [RE-wrenches] battery venting

2011-12-31 Thread Roy Butler
I agree with Michael. I would try to avoid pressurized battery boxes. I also want to add that I have always followed the 360 degree limit for vent pipe bends. I have also learned that even though the Zephyr vents can be replaced, most of them run so quietly that most end users don't notice wh

Re: [RE-wrenches] battery venting

2011-12-31 Thread Michael Welch
Exeltech wrote at 02:16 PM 12/31/2011: >4) Install the vent fan on the fresh-air inlet side of the box. Not a recommended practice. This pressurizes the box, so that the gas can exit through any leaks into the room just as easily as up the vent. So instead, the fan should be an exhaust fan,

Re: [RE-wrenches] battery venting

2011-12-31 Thread Exeltech
e if it *should* fail. Happy New Year to all. Dan > --- On Sat, 12/31/11, Richard L Ratico > wrote: > > From: Richard L Ratico > Subject: Re: [RE-wrenches] battery venting > To: re-wrenches@lists.re-wrenches.org > Date: Saturday, December 31, 2011, 1:47 PM > Huh?

Re: [RE-wrenches] battery venting

2011-12-31 Thread Dave Palumbo
:47 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] battery venting Huh??? I'm probably missiing something here. What happens when the powervent fails??? I replace it with another, the same thing I do when other equipment in our whiz bang industry fails. The difference wit

Re: [RE-wrenches] battery venting

2011-12-31 Thread Richard L Ratico
Huh??? I'm probably missiing something here. What happens when the powervent fails??? I replace it with another, the same thing I do when other equipment in our whiz bang industry fails. The difference with the powervent is that it is easy and relatively inexpensive. I've also had good luck using

[RE-wrenches] battery venting

2011-12-31 Thread JRQ
in those parameters? Jeffrey Quackenbush NABCEP Certified PV Installer Peripatetic Solar Technician From: Allan Sindelar To: re-wrenches@lists.re-wrenches.org Sent: Saturday, December 31, 2011 8:42 PM Subject: Re: [RE-wrenches] battery venting Jeff, I would use a P

Re: [RE-wrenches] battery venting

2011-12-31 Thread Kent Osterberg
Jeffrey, I'll second Jay's suggestion that sealed AGM batteries are the best choice in this circumstance. Presumably this is a grid backup system so the poor endurance of AGMs for cycling applications shouldn't be an issue. If you use a Zephyr power vent horizontal runs shouldn't be problem,

Re: [RE-wrenches] battery venting

2011-12-31 Thread Ray Walters
I, 2nd Allan's recommendation, or better, use sealed batteries, since its battery backup, and so small. People are bad about battery maintenance on anything but off grid. You definitely can't afford to have hydrogen sulfide going up through the building. Ray Walters On 12/31/2011 8:12 AM, A

Re: [RE-wrenches] battery venting

2011-12-31 Thread Jay Peltz
I would recommend sealed batteries for this application. Jay Peltz Power Sent from my iPhone On Dec 31, 2011, at 6:59 AM, JRQ wrote: > Wrenches, > > I'm looking at a potential battery backup system wtih a 200 AH @48V flooded > battery bank in the basement electrical room of a 3 story buildi

Re: [RE-wrenches] battery venting

2011-12-31 Thread Allan Sindelar
Jeff, I would use a Power Vent by Zephyr Industries. In addition to a 12V or 48V fan, his units have a built-in backdraft damper. Negative building pressure under certain conditions would be a concern of mine, so I wouldn't rely on angle to ensure exhaust always travels

Re: [RE-wrenches] battery venting

2011-12-31 Thread JRQ
Wrenches, I'm looking at a potential battery backup system wtih a 200 AH @48V flooded battery bank in the basement electrical room of a 3 story building. There is a window in the electrical room. The batteries will be located about 10' from an outdoor wall. The building is all reinforced concre

[RE-wrenches] Battery Venting

2010-12-14 Thread Kent Osterberg
Fellow Wrenches, The discussion about battery venting reminds me of a useful and inexpensive program, BattMV, for determining ventilation requirements per EN-50272.  EN-50272 is a European standard used to determine how much air flow is needed for a room, I don't know of a equivalent standard