HI Dave and Chris,
Good points, however.
I’ve had radian board failures which shut it all down. You are correct if a
power module goes down then it will still continue working.
This project doesn’t need telecomm redundancy but close.
And if the inverter shuts down then the AGS won’t star
I think so also for the same reason Chris! So I guess I don't understand
why you need the external transfer switch Jay?
Is not the internal radian transfer switch the less is more for offgrid?
--Dave
> I think Radians are redundant anyway, if you parallel the output they will
> keep going when o
Hi Jay,
I've been using the ASCO Series 185 for years with the Radian, single or
dual. With some fine tuning I've gotten the transfer time down to around 1
second. The have a manual switch built inside of it. They also offer a
service rated (with CB) or not. Zero failures to date.
Christopher
On
I think Radians are redundant anyway, if you parallel the output they will
keep going when one fails. Also, the 8KW are two x 4KW modules, both can
function independently. I know this because we lost one at home and kept
going until a replacement arrived.
On Thu, Jan 11, 2018 at 7:03 PM, jay wrot
HI all,
I’m doing a project with 2 radians in a redundant configuration.
Each one would go into a transfer switch to power the common load.
I’m looking for a good, fast transfer switch. 30amp 120/240 is fine.
And maybe a mechanical feature as well.
Code isn’t an issue
Will be off grid, remote