Re: [RE-wrenches] Surge arrestors on strings

2018-10-10 Thread b...@midnitesolar.com
The SPD-600 is evidently the one to use on the SMA TL inverters. In older grounded PV systems, if the negative or positive is grounded directly to ground, then you could get by without an SPD connected to that grounded conductor because it is, well, already grounded and that line will rise in

Re: [RE-wrenches] Surge arrestors on strings

2018-10-09 Thread Dave Angelini Offgrid Solar
We have been using Midnite SPD's since they came out. The one suggestion I have is the light is too intense. I have clients who have covered the SPD's in tape to keep the light from attracting small flying insects to the electronics area. Some places just have too many bugs :( The blue seems to b

Re: [RE-wrenches] Surge arrestors on strings

2018-10-09 Thread Bill Battagin
boB,             To add to Drake's  wonderings, I've had a few SMA TL-40 inverters trip with an AFCI fault.  Significant hassle to get onsite and deal with it. Some with metal roofs some without, may have been lightening in the area. Bill On 10/9/2018 2:02 PM, Drake wrote: Hi boB, I will

Re: [RE-wrenches] Surge arrestors on strings

2018-10-09 Thread Drake
Hi boB, I will keep putting an SPD on each string and on the AC line. Sometimes my systems end up with a lot of blue lights hanging from a wiring gutter! Have you ever heard of any problems using the Midnite SPDs with Sunny Boy TL series inverters? So far, I don't think I've had a problem,

Re: [RE-wrenches] Surge arrestors on strings

2018-10-09 Thread b...@midnitesolar.com
For an inverter with two MPPT inputs, you will need to treat the negatives and positive lines separate unless the manufacturer says something else.  That means one  SPD per array unfortunately.  Negative and positive connect to separate leads of the SPD and then ground in the middle.  As both

Re: [RE-wrenches] Surge arrestors on strings

2018-10-09 Thread cwarfel
I think something on the order of 90+% lightning strikes come from the utility feed, not the dc side. That has to be ignored if in a high strike area orgrid isolated. On 10/8/2018 10:37 PM, Ray wrote: I believe you can use the SPD 300 AC on 2 strings, if PV neg is grounded.  You would conne

Re: [RE-wrenches] Surge arrestors on strings

2018-10-08 Thread Ray
I believe you can use the SPD 300 AC on 2 strings, if PV neg is grounded.  You would connect the green to ground (or PV neg) and then connect the red to one string pos, and connect the black to the other string pos.  This would be limited to 300 v also.  I haven't tried that exact configuration

[RE-wrenches] Surge arrestors on strings

2018-10-08 Thread Drake
Hello Wrenches, Do you use surge arrestors with multi MPPT input string inverters? Do you put a separate arrestor on each MPPT input? I find it sort of pricey using a Midnite Solar arrestor on each string, but have been doing that. Is there a less expensive approach that is effective? I beli