Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-12 Thread Mac Lewis
Hi William, One other thing. Remember to specify the 50mV shunt. "225.01 BatCurSnsTyp". I believe that means it will drop 50 mV across the shunt with 500A current throughput. It's this proportion that determines the value for 225.03 BatCurGain. In your case, that should be 50, but I think it

Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-12 Thread Mac Lewis
Hi William, Yes the Outback shunt should be fine for this application. See page 72 here for the calibration: http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-20.pdf As far as verifying with your clamp meter, I'd say if you can verify within 15% (remember to check polarity) then it is properly ca

Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-12 Thread William Miller
Mac: Thanks for the advice. We will install the shunt today. A few more questions: 1. Will the Outback 50ma shunt be compatible. My research indicates the value is correct. 2. DC clamps are notoriously inaccurate, particularly at low amperages. Will this be a problem, or is shorting the lea

Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-12 Thread William Miller
Mac > On Feb 12, 2015, at 4:45 AM, Mac Lewis wrote: > > Hi William, > > I want to talk directly to your problem at hand. I think installing the > shunt and properly calibrating it, will fix this system . In a DC coupled > system with a Sunny Island, it is imperative that you use a shunt,

Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-12 Thread Mac Lewis
Hi William, I want to talk directly to your problem at hand. I think installing the shunt and properly calibrating it, will fix this system . In a DC coupled system with a Sunny Island, it is imperative that you use a shunt, unless you are using the Midnite charge controllers with the communicat

Re: [RE-wrenches] Sunny Island Failure and various related issues

2015-02-11 Thread Ray Walters
Hi William; Yes I'm getting too old to let manufacturers off the hook anymore. They just don't pay me enough (wink, maybe if I ever was compensated for service calls?) Unfortunately I have had the exact same experience with SMA's phone tech support. I was having setup issues that were not co

[RE-wrenches] Sunny Island Failure and various related issues

2015-02-11 Thread william
Friends: I have an existing service issue with a Sunny Island 4548 system shutting down unexpectedly. The system is off-grid with generator, two inverters, DC coupled charging. The batteries are a set of used Full River VRLA L-16s (3 strings of 8). We tested the at-rest battery voltages and