Wallace: William is correct, a PV System is NOT a SDS. If you're installing a "TL" or transformerless string inverter, a DC GEC from the inverter is NOT required, only a properly sized EGC. With Micro-inverters, if the PV+ or PV- has a ground reference in the micro-inverter, such as an Enpha

Re: [RE-wrenches] PV GEC

2013-11-09 Thread William
W: A string inverter does not constitute a separately derived system unless it is transformer isolated. The recreating of the neutral is what creates an SDS. Your GEC, if required, stops at the inverter. It is not always required, i.e. Enphase M250. William Miller > On Nov 9, 2013, at 1:53

[RE-wrenches] PV GEC

2013-11-09 Thread Wallace W. Weeks
Wrenches, On a recent install I've come across a question I would like to get your thoughts on. In regards to running a GEC on a "separately derived power system", more specifically A single phase 600 v residential PV system with a string inverter. >From my past experience and building from

Re: [RE-wrenches] PV GEC to the same point as theutilityservice GEC?

2010-08-24 Thread Hans Frederickson
that live in areas where lightning is rare, so I can stop hating it. Regards, -Hans _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray Walters Sent: Monday, August 23, 2010 1:55 PM To: RE-wrenches Subject: Re: [RE-wr

Re: [RE-wrenches] PV GEC to the same point as the utilityservice GEC?

2010-08-23 Thread R Ray Walters
> I hope this helps clarify it for you. > > Matt Lafferty > gilliga...@gmail.com > > > > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szrom > Sent: Monday, August 23, 2010 6:41 AM > To

Re: [RE-wrenches] PV GEC to the same point as the utilityservice GEC?

2010-08-23 Thread Matt Lafferty
nches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szrom Sent: Monday, August 23, 2010 6:41 AM To: RE-wrenches Subject: Re: [RE-wrenches] PV GEC to the same point as the utilityservice GEC? Matt, Thanks for the reply. I should have clarif

Re: [RE-wrenches] PV GEC to the same point as the utility service GEC?

2010-08-23 Thread Jason Szrom
e-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Matt Lafferty Sent: Thursday, August 19, 2010 2:01 PM To: 'RE-wrenches' Subject: Re: [RE-wrenches] PV GEC to the same point as the utility service GEC? Good questions, Jason. No. Yes

Re: [RE-wrenches] PV GEC to the same point as the utility service GEC?

2010-08-19 Thread Matt Lafferty
ot; Matt "I'm no building inspector" Lafferty _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szrom Sent: Thursday, August 19, 2010 7:38 AM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] P

[RE-wrenches] PV GEC to the same point as the utility service GEC?

2010-08-19 Thread Jason Szrom
Wrenches, Questions: Does the PV GEC have to be bonded to the ground electrode system at the same point as the utility service equipment GEC? Is there a code section to back this up? Additional info: 1. The DC side of the inverter is a separately derived system and therefore needs a GE