Allan,
I have a recent power issue come up with a Magnum inverter. A customer
tried to operate her Splindide washer/dryer but the motor would not
start. I looked at the waveform with a scope and RMS voltage and
frequency were fine. The waveform looked good until the motor tried to
start.
Seems that I remember that the APC and other backups are not a sine wave but
a modified wave? But it's been a while.
Bob
On Wed, Feb 11, 2009 at 9:52 AM, Howie Michaelson wrote:
> I installed an off-grid system with identical symptoms:
>
> OB VFX 3648 dual stack
> Buderus GB142-24
> Kohler 12 kW
Wrenches,
Thank you to you Wrenches who have responded. Keep them coming; I'm
collating all as part of our customer support on this. We have several ideas
to try out.
Darryl, it's not excessive draw. I had a Kill-a-Watt on the AC input during
on-site testing. I saw a momentary peak of 360W (for al
nches] Magnum MS4448AE Compatibility Question
I installed an off-grid system with identical symptoms:
OB VFX 3648 dual stack
Buderus GB142-24
Kohler 12 kW propane genny
The boiler runs fine on the inverter power, but will occasionally error out
(6A) and shut down while the generator is ru
I dont' know if you can power just the part this is giving problems
and not the big load which is pumping?
but had a similar problem with an SW trace.
I installed a Exeltech inverter to power that load specifically and
ever since has worked fine.
The guys at Exeltech make a wave form that ev
I installed an off-grid system with identical symptoms:
OB VFX 3648 dual stack
Buderus GB142-24
Kohler 12 kW propane genny
The boiler runs fine on the inverter power, but will occasionally error
out (6A) and shut down while the generator is running (usually after it
has been on for hours). The p
shape.
Darryl
--- On Wed, 2/11/09, boB Gudgel wrote:
> From: boB Gudgel
> Subject: Re: [RE-wrenches] Magnum MS4448AE Compatibility Question
> To: "RE-wrenches"
> Date: Wednesday, February 11, 2009, 12:03 AM
> Peter Parrish wrote:
> >
> > As an old
31 PM
*To:* al...@positiveenergysolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Magnum MS4448AE Compatibility Question
Hi Allan,
This is not an unusual problem. i have seen it with conventional
forced air heating systems. The burner controls would not run on A
Xantrex or Outback sine wave inv
enches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Monday, February 09, 2009 9:31 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] Magnum MS4448AE Compatibility Question
Hi Allan,
This is not an unusual problem. i have se
David Katz wrote:
Hi Allan,
This is not an unusual problem. i have seen it with conventional
forced air heating systems. The burner controls would not run on A
Xantrex or Outback sine wave inverter. There is something about
waveforms from inverters designed by Trace legacy engineers. I had
Hi Allan,
This is not an unusual problem. i have seen it with conventional forced
air heating systems. The burner controls would not run on A Xantrex or
Outback sine wave inverter. There is something about waveforms from
inverters designed by Trace legacy engineers. I had to put in Exeltech
Have you tried a different SW inverter at the site? There is a
difference between brands.
Also, have you tried a "clean" wave form gennie like the Honda
inverter series.
Finally I don't think that most manufacturers will guarantee that
their wave form will power a specific load.
Regards
I wonder if a work around might be to run the igniter off a relay activated
by the original board and fed by the inverter direct?
I have seen things not start when the charger was drawing off the generator,
not Magnums but old Hearts.
Bob
On Mon, Feb 9, 2009 at 1:16 PM, Allan Sindelar <
al...@po
I use a lot of these Magnum 4448's and have never had any trouble like that. i
did have some real odd behavior out of the first 3 i installed and we worked
with magnum to get a software upgrade that would handle surge better.
Mine where falling off for a lenghtly period of time when a heavy load
I second Dana's response. I have observed that the MS4448 waveform
quality degenerates quite rapidly with imbalanced loading of one or
the other of the 120 volt output legs. I can't give a quantitative
(% distortion/amps) number to it, but I would classify it as
severe. I first noticed it wh
e-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Monday, February 09, 2009 11:16 AM
To: RE Wrenches
Subject: [RE-wrenches] Magnum MS4448AE Compatibility Question
Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
Wrenches,
We have an unusual problem, and I need to know if anyone else has had this
or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional: 1,800W
PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16 S-460s,
installed summer 2008.