Unglazed solar pool heaters are typically sized based on surface area, not gallons, because most of the heat loss occurs at the surface. They are rated in daily BTU output, but the test condition rating can be deceiving. You are really trying to overcome the loss of heat in the long-term, not heat

Re: [RE-wrenches] Heat Exchangers Topic for Swimming Pools

2015-04-06 Thread Gary Willett
1 BTU = energy required to heat 1 lb of water 1 degree F in 1 hour 1 gallon of water = 8.34 lbs @ 62F 15000 gal water = 125,100 lbs A 100 kBTU heater would heat the pool about 0.7F per hour. Sent from my iPhone 5s > On Apr 5, 2015, at 7:49 PM, Jay wrote: > > Hi Tom > > Is your doubling of

Re: [RE-wrenches] Heat Exchangers Topic for Swimming Pools

2015-04-05 Thread Jay
Hi Tom Is your doubling of the HE an rule of thumb or is there a formula? As to system information. 510 sq ft collector 100,000 btu HE ( main problem I think) 70,000 gal pool Uncovered ( other main problem. ) The problem is that it's not getting the pool warm. Thanks for all the help and ad

[RE-wrenches] Heat Exchangers Topic for Swimming Pools

2015-04-05 Thread Tom Lane
Most heat exchangers for swimming pools are designed for boilers delivering 140F or 190F as a heat source based on the size and/ or the number gallons in the pool . The solution for a low temperature source like solar in order to keep the approach temperature low to the flat plate collectors ( a