Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-15 Thread Andrew Truitt
Regarding the DC disco issue, we have identified the 3-pole, 600Vdc rated, 200A Crouse-Hinds CH364R ( http://www.crouse-hinds.com/crousehinds/newproducts/relatedinfo/Solar%20Combiner%20Brochure%20110309.pdf) as a replacement for the Square D version. Its a little pricey but it looks like the best

Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-14 Thread Philip Boutelle
Kirpal and Wrenches, Can you describe your battery setup with the four Sunny Islands? SMA recommends using two parallel 1/0 conductors to each SI DC disconnect, for three reasons: wire fill limitations with the 1.5" knockouts they provide, ease of landing in the breaker, and because the 125A break

Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-11 Thread Kirpal Khalsa
Davethis is exactly what the sunny island is capable of.supply the house panel from the sunny island output, and the main panel in the barn to the input side, the house panel will run full time via the sunny islands, install a MANUAL transfer switch for times when the sunny islands may need

Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-11 Thread Richard L Ratico
Hi Dave, Depending on the house loads, you might very well do without an additional (very expensive) auto transfer switch. The inverters, of course, already have one. Just leave the Sunny Islands connected 24/7. The transfer from grid to battery is then milliseconds and flawless. The 56 amps cont

Re: [RE-wrenches] Grid-tie Sunny Island

2010-04-11 Thread Dave Palumbo
We have a new (for us) application for grid connected net-metered PV with battery back-up as follows. The twist is that the entire load center in the house will be the "protected loads panel". - 5kW PV ground mount located 250 feet East of their barn. - Will utilize AC Coupled