Re: [RE-wrenches] GEC tap

2025-02-20 Thread Drake Chamberlin via RE-wrenches
Crimp on "C" clamps meet code, but sometimes are not that secure of a connection. _Drake Chamberlin_ _Athens Electric LLC_ _Ohio Electrical Contractor's License 44810_ _NABCEP Certified PV Installation Professional_ --- On 2025-02-20 12:01, Kristopher Schmid via RE-wrenches wrote: Than

Re: [RE-wrenches] GEC tap

2025-02-20 Thread Jason Szumlanski via RE-wrenches
Around here, AHJs require that the GEC is not connected to the service disconnect or any supply-side interconnected PV AC disconnect. They require a GEC from the meter socket enclosure to the GE system with a N-G bond in the meter enclosure (the N and G lugs are one and the same typically anyway in

Re: [RE-wrenches] GEC tap

2025-02-20 Thread Kristopher Schmid via RE-wrenches
Thanks Cory, I think that the supply side connection may require the irreversible splice since it is considered a service entrance. In some cases, the GE is not easily accessible (under concrete for example) to add a GEC to the GE directly. In any case, my AHJs do not like the split bolt connect

Re: [RE-wrenches] GEC tap

2025-02-19 Thread Corey Shalanski via RE-wrenches
Kris, As far as I know, taps to GECs need not be irreversible. I believe you might be thinking of the NEC 250.64(C) requirement for GECs to be installed "in one continuous length" or otherwise be spliced together via one of several options, with one option being to use irreversible compression-typ

Re: [RE-wrenches] GEC tap

2025-02-19 Thread August Goers via RE-wrenches
Hi Kris - We use C-taps all the time - if you search for c-tap connector you'll see plenty of results with Burndy being a big player in the market. Depending on your wire sizing, you might be able to use the thin wall variant which requires a smaller tool and overall are lower cost. If you need to

[RE-wrenches] GEC tap

2025-02-19 Thread Kristopher Schmid via RE-wrenches
Hi All, What are you all using for an "irreversible" tap to an existing GEC? I have been looking at compression CTAPs. Do they require a special crimper die? Thanks, Kris Shine On! Kris Schmid Legacy Solar, LLC 137 West 1st Avenue Luck, WI 54853 www.legacysolar.com 715-653-4295 NABCEP Certif