2012-12-24 Thread Drake
Hello Wrenches, I have an inquiry from the owners of an existing system with a Fronius IG Plus 10.0-1 that is looking for backup power. Due to the output Fronius, I'm thinking the best solution would be to AC couple a pair of Sunny Islands to the Fronius. Has anyone tried this combination?

Re: [RE-wrenches] Fronius IG Plus line

2009-12-26 Thread Drake Chamberlin
At 03:26 AM 12/26/2009, you wrote: was brooks talking about the plus line? I think not. I think that thread was regarding the Fronius IG The post is copied below. I would like to know it the problem extends to the Plus line. Bill Brooks

[RE-wrenches] Fronius IG Plus line

2009-12-26 Thread Nick Vida
was brooks talking about the plus line? I think not. I think that thread was regarding the Fronius IG the thread was: Efficiency Curves of Fronius Inverters? ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenche

Re: [RE-wrenches] Fronius IG Plus line

2009-12-24 Thread Drake Chamberlin
ent: Friday, December 18, 2009 8:03 PM To: RE-wrenches Subject: Re: [RE-wrenches] Fronius IG Plus line Marco, My only comment is the 3 phase units are a long lead time item. Fronius expects to catch up to demand by end of Q1 2010. Carl SunRock Solar On Thu, Dec 17, 2009 at 6:55 PM, Marco

Re: [RE-wrenches] Fronius IG Plus line

2009-12-19 Thread Doug Pratt
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams Sent: Friday, December 18, 2009 8:03 PM To: RE-wrenches Subject: Re: [RE-wrenches] Fronius IG Plus line Marco, My only comment is the 3 phase units are a long lead time item. Fronius expects to catch up to demand by e

Re: [RE-wrenches] Fronius IG Plus line

2009-12-18 Thread Carl Adams
Marco, My only comment is the 3 phase units are a long lead time item. Fronius expects to catch up to demand by end of Q1 2010. Carl SunRock Solar On Thu, Dec 17, 2009 at 6:55 PM, Marco Mangelsdorf wrote: > I have yet to install a Fronius IG Plus inverter. Looking through the > manual I’m t

Re: [RE-wrenches] Fronius IG Plus line

2009-12-17 Thread David Brearley
Marco, They are all single-phase, with the exception of the IG Plus 11.4-3 and 12.0-3, which are 3-phase units. David Brearley, Senior Technical Editor SolarPro magazine NABCEP Certified PV Installer  david.brear...@solarprofessional.com Direct: 541.261.6545 Fax: 541.512.0343 Visit our Web si

[RE-wrenches] Fronius IG Plus line

2009-12-17 Thread Marco Mangelsdorf
I have yet to install a Fronius IG Plus inverter. Looking through the manual I'm trying to determine whether each inverter in the line, between 3 and 12 kW, puts out three-phase power across all three poles, L1, L2 and L3 or whether all or some of these models put out power across just one or two

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-28 Thread Phil Undercuffler
> > > > > > > > > > > > > > > On Sat, Jun 27, 2009 at 9:22 PM, > > Darryl Thayer > > wrote: > > > > > > > > Again this is FMI for my information, Did not Square D > > change there rating for PV systems? >

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-27 Thread Darryl Thayer
use the double break I am limited to 18 amps in all cases. Darryl Correct? --- On Sat, 6/27/09, Phil Undercuffler wrote: > From: Phil Undercuffler > Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA??? > To: "RE-wrenches" > Date: Saturday, June 27,

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-27 Thread Phil Undercuffler
rmation, Did not Square D change there rating > for PV systems? > Darryl > > --- On Fri, 6/26/09, Phil Undercuffler wrote: > > > From: Phil Undercuffler > > Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA??? > > > > > This confirmed my

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-27 Thread Darryl Thayer
Again this is FMI for my information, Did not Square D change there rating for PV systems? Darryl --- On Fri, 6/26/09, Phil Undercuffler wrote: > From: Phil Undercuffler > Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA??? > > This confirmed my understa

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-26 Thread Phil Undercuffler
Previous message This confirmed my understanding that the limiting factor on the 30A switch in a photovoltaic applications is not 30A * 0.8. The limiting factor is 18A per pole or 11.5A Isc per pole. To clarify – the 18A per pole / 11.5A Isc per pole only applies if you are using the lim

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???(Mark Frye)

2009-06-21 Thread Mark Frye
ts.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of g...@remotepowerinc.com Sent: Sunday, June 21, 2009 1:00 PM To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA???(Mark Frye) Mark, Would you mind posting a link - if you

Re: [RE-wrenches] fronius IG Plus practical engineering WAA??? (Mark Frye)

2009-06-21 Thread greg
Mark, Would you mind posting a link - if you have it - to the Data Bulletin on the HU361 you spoke of? I'm sure I can find it on the Sq D site if you don't Thanks! Greg Egan > Date: Sun, 21 Jun 2009 09:22:43 -0700 > From: "Mark Frye" > Subject: Re: [RE-wrench

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-21 Thread Mark Frye
ar.com _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob-O Schultze Sent: Saturday, June 20, 2009 2:36 PM To: RE-wrenches Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA??? Nick, Fronius sells a heavy

[RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-21 Thread Tom DeBates
We recently installed an IG Plus 7.5. Since we were combining 8 strings, and the IGPlus has provision for 6 strings, we needed combine the strings before the inverter. The buss bars at the inverter allowed us to do this quite nicely. The inverter (at least in our case) came out-of-the-box with "

[RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-20 Thread Nick Vida
guys, thanks for your input. I didnt know about the add on. glad to see it is out there. thanks again Nick Vida ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wr

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-20 Thread Bob-O Schultze
Nick, Fronius sells a heavy copper buss bar which will link all the six inputs together. They look sort of like the Outback PSPV bus bars except copper and MUCH heavier. If you need four or more inputs you'll need to get two of them. Three or less, cut one in half. For some reason known o

Re: [RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-20 Thread Allan Sindelar
Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com _ From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Vida Sent: Saturday, June 20, 2009 1:23 PM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenc

[RE-wrenches] fronius IG Plus practical engineering WAA???

2009-06-20 Thread Nick Vida
hey Wrenches. I opened my soon to be installed fronius IG Plus to see what was going on in there, and found myself a bit disappointed. There is a 6 string combiner in there which is fine, however there is no bypass for the fusing section and the terminals are rated at 20 amps. In a situation wh

Re: [RE-wrenches] Fronius IG Plus

2009-04-19 Thread Kelly Keilwitz, Whidbey Sun & Wind
Marco, Just installed a 7.5 last week, our first. We have a 10K and a 4K in the shop waiting to go up. I'm impressed with the design - it's obvious that a lot of thought went into it. And, it's so nice not to lift a lot of copper :) We'll have to stay tuned on the energy production and reliabil

[RE-wrenches] Fronius IG Plus

2009-04-18 Thread Marco Mangelsdorf
Any of you have experience with the new Fronius IG Plus inverters in the 8 kW to 12 kW range? Good, bad, beautiful, ugly? Thanks, marco Marco Mangelsdorf, President 69 Railroad Avenue, A-7 Hilo, Hawai'i 96720 (808) 969-3281, 934-7462 facsimile www.provision-solar.com ___

Re: [RE-wrenches] Fronius IG Plus

2009-01-18 Thread Ohs
Yes, Conergy has stock or availability of their products. Jason Lombard CSBA Open Hand Solar 505 795 8646 On Jan 17, 2009, at 12:16 AM, "Marco Mangelsdorf" wrote: Does anyone know if Fronius is actually shipping their higher output IG Plus line? Do any distributors actually have some o

[RE-wrenches] Fronius IG Plus

2009-01-16 Thread Marco Mangelsdorf
Does anyone know if Fronius is actually shipping their higher output IG Plus line? Do any distributors actually have some on their shelves? Thanks, marco Marco Mangelsdorf, Ph.D., President Electrical Contractor License C-26351 69 Railroad Avenue, A-7 Hilo, Hawai'i 96720 (808) 969-3281, 934-7462