ski
To: re-wrenches@lists.re-wrenches.org
Sent: Tuesday, July 15, 2014 3:43 PM
Subject: Re: [RE-wrenches] Concentrics at 250 volts plus
Related question: How should we treat circuits that are less than 250V? Does
the EMT need to be bonded at EITHER end?
Some of our local inspectors are requ
On Tue, Jul 15, 2014 at 12:45 PM, wrote:
>
> Message: 3
> Date: Mon, 14 Jul 2014 15:11:44 -0700
> From: William Miller
> To: RE-wrenches
> Subject: [RE-wrenches] Concentrics at 250 volts plus
> Message-ID: <52645f97-f231-4149-a8fd-d2e44e315...@millersolar.com>
nches'
*Subject:* Re: [RE-wrenches] Concentrics at 250 volts plus
Kelly:
Just as I suspected. I wish you could be here to share the lunch I have
earned on my bet.
Thanks,
William
[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-56
E-wrenches'
Subject: Re: [RE-wrenches] Concentrics at 250 volts plus
Kelly:
Just as I suspected. I wish you could be here to share the lunch I have earned
on my bet.
Thanks,
William
[Gradient Cap_mini]
Lic 773985
millersolar.com<http://www.millersolar.com/>
805-438-5600
From: R
rg] On
Behalf Of Kelly Larson
Sent: Monday, July 14, 2014 10:16 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Concentrics at 250 volts plus
Hi William,
The requirement for bonding on BOTH ends comes when the wire though the
conduit is a GEC. For EGC, just one end of the conduit is suff
Hi William,
The requirement for bonding on BOTH ends comes when the wire though the conduit
is a GEC. For EGC, just one end of the conduit is sufficient.
Blessings,
Kelly
~
Kelly Larson
707-223-3209
Box 504
Ukiah, CA 95482
Electrical Engineer
NABCEP Certified Solar PV Installation Profes
Friends:
Please help us settle a crew debate before we come to blows: for circuits 250
volts and higher, do we need to bond EMT at both ends? Or, if there is bonded
cabinet with a concentric on one end and a solid, bonded metal cabinet on the
other, do we need a bonding bushing on the concent