Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-20 Thread Carl Adams
> > -Original Message- > From: re-wrenches-boun...@lists.re-wrenches.org > [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click > Sent: Thursday, April 19, 2012 1:39 PM > To: re-wrenches@lists.re-wrenches.org > Subject: Re: [RE-wrenches] Combining Solectr

Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-19 Thread Dave Palumbo
@lists.re-wrenches.org Subject: Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000 This is fine; your PVI2500 is rated for 10.4A, while the SB3000 is 12.5A. You can put up to 24A rated current through your 30A fuses. Though the disconnect isn't technically a service disconnect

Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-19 Thread Dave Click
This is fine; your PVI2500 is rated for 10.4A, while the SB3000 is 12.5A. You can put up to 24A rated current through your 30A fuses. Though the disconnect isn't technically a service disconnect, I'd recommend using a 60A rated (fused at 30A) disconnect per 230.79(D). You would run a neutral to

Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000

2012-04-19 Thread Dave Palumbo
Wrenches, We have an installation in place since 2008 working well with a Solectria PVI 2500 feeding a supply side grid connection. Homeowner wants us to double the system size now. I can buy a SB3000 inverter for $ 300 less than the Solectria PVI 2500 (with upcharge for 10 yr warranty) and I