> -Original Message-
> From: re-wrenches-boun...@lists.re-wrenches.org
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
> Sent: Thursday, April 19, 2012 1:39 PM
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] Combining Solectr
@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Combining Solectria PVI 2500 with SB3000
This is fine; your PVI2500 is rated for 10.4A, while the SB3000 is 12.5A.
You can put up to 24A rated current through your 30A fuses.
Though the disconnect isn't technically a service disconnect
This is fine; your PVI2500 is rated for 10.4A, while the SB3000 is
12.5A. You can put up to 24A rated current through your 30A fuses.
Though the disconnect isn't technically a service disconnect, I'd
recommend using a 60A rated (fused at 30A) disconnect per 230.79(D). You
would run a neutral to
Wrenches,
We have an installation in place since 2008 working well with a Solectria
PVI 2500 feeding a supply side grid connection.
Homeowner wants us to double the system size now. I can buy a SB3000
inverter for $ 300 less than the Solectria PVI 2500 (with upcharge for 10 yr
warranty) and I