I checked into the PRI strategy a few months back. An Outback
applications engineer responded that while they were collaborating with
SolarEdge at one time on the method, they don't recommend it any longer
and were going to pull the tech note. The response also questioned
whether SolarEdge stil
Hi Gary,
These Solar Edge inverters can use radio ripple control to change power
output. Its a simple control strategy that allows control of the power
output presumably from a grid-operator. You would need to enable the
RRCR. Here is a paper about that
http://www.solaredge.com/sites/default/fi
Maverick:
Thanks for responding. You've been very helpful in the past with
my battery based solution questions.
Daily load demand from the Protected Loads Panel is about 10kWh.
With 5 average daily peak sun hours, and 75% charging efficiency,
the batte
How many kWh are you shooting for?
> On Oct 17, 2016, at 9:54 PM, Gary Willett
> wrote:
>
> Esteemed Wrenches:
>
> Anyone have experience setting up AC coupling with SolarEdge and the Outback
> Radian?
>
> I have a client with a SolarEdge SE1A-US inverter, equipped with 31
> SunPower
It looks like way too much power to AC couple
with a 4KW Radian. Be sure to talk to an Outback
engineer in great detail before using the GSLC175AC-120/240.
At 10:54 PM 10/17/2016, you wrote:
Esteemed Wrenches:
Anyone have experience setting up AC coupling
with SolarEdge and the Outback Radian?
Esteemed Wrenches:
Anyone have experience setting up AC coupling with SolarEdge and the
Outback Radian?
I have a client with a SolarEdge SE1A-US inverter, equipped with
31 SunPower X21-345 modules (10.7kWp) and associated SolarEdge P400
DC optimizers. Th