-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake
Sent: Friday, March 08, 2013 9:40 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupled Magnum Issue
Thank you to all who responded to this post.
Larry, that sounds like a great potential
Thank you to all who responded to this post.
Larry, that sounds like a great potential solution. That will put the
frequency shift in line with where the battery cutoff voltage needs
to be. The frequency shift happens 2 volts above the absorption
charge set point. My only issue with the soluti
Solar Power Systems
Sent: Thursday, March 07, 2013 3:36 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupled Magnum Issue
ANDyou are still working on that stand-alone, programable,
temperature compensated battery chargerright???
Thank you,
Larry Crutcher
Starlight Solar Power
ANDyou are still working on that stand-alone, programable, temperature
compensated battery chargerright???
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Mar 7, 2013, at 4:07 PM, Brian Faley wrote:
Hi Allan,
In answer to your question: Yes, we’re developing an AC side 4k
nches] AC Coupled Magnum Issue
McAfee SiteAdvisor Warning
This e-mail message contains potentially unsafe links to these sites:
<http://www.siteadvisor.com/sites/athens-electric.com/?pip=false&premium
=true&client_uid=446795512&client_ver=3.6.0.187&client_type=IEPlu
OK, a bit more:
The line diagram I was referencing was dated 5/1/2010. A later
diagram from a Powerpoint given at last year's NABCEP CE
conference shows a "MagNet" AC diversion controller. It allows AC
diversion loads and three-stage charging. No mention of temp c
Meant to say, "You should tweak #3 & #4 above..."
Drake,
Charging an AGM battery does not have to occur at the maximum charge voltage
allowable; you can charge at a lower voltage for longer periods of time and
still achieve 100% SoC. Since you have grid power to work with, slow down the
charg
Drake,
Magnum's approach does not use disconnecting the AC output from
the GT inverter as a fail-safe method of preventing battery
overcharge. Rather, the Magnum documents I have use a DC diversion
controller and diversion load for this purpose. Their method
Drake,
Charging an AGM battery does not have to occur at the maximum charge voltage
allowable; you can charge at a lower voltage for longer periods of time and
still achieve 100% SoC. Since you have grid power to work with, slow down the
charge cycle.
Assuming you have a late model ME-RC and v
Hello Wrenches,
I had an unexpected glitch in AC coupling a Magnum 4024 PAE
inverter. The system utilizes AGM batteries, which (according to
Concorde tech support) have a very strict upper voltage limit.
The relay used to stop the current input from the direct grid tie
inverter, when batter