I have felt for some time that inverters should have a logic control to
turn them off. "Short contact A to ground to disable inverter" type of
interface. If we had that, we could implement generator protection very
simply.
For your application, I see these being used in 3 phase pump control
system
Real simple. A contactor with a phase loss detector gadget.
Chris Mason
Comet Systems
Anguilla (264) 235-5670
St. Kitts (869) 662-5670
skype netconcepts
NABCEP Certified Solar PV Installerâ„¢
Renewable Energy Systems professional
Generac Generators Factory technician
On Sep 24, 2013 11:12 AM, "Kar
Eaton just announced some safety switches with shunt trip that may work
for you- Google: Eaton TD008003EN to get the datasheet.
TD008003EN
On 2013/9/24 11:12, Karl Jaeger wrote:
Greetings Esteemed Wrenches,
We are building a 35.75kW project with (6) Power One 6000's. The
service is a 240 del
Phase loss relay that opens contactor(s) serving the inverters. That will
shut everything down if the utility drops a phase.
-James Jefferson Jarvis
APRS World, LLC
http://www.aprsworld.com
+1-507-454-2727
(this message was sent from my cell phone ... my apologies for any spelling
errors)
On Sep
Greetings Esteemed Wrenches,
We are building a 35.75kW project with (6) Power One 6000's. The service is a
240 delta. The utility is requiring (late in the game) that if one leg of the
service is lost, all inverters must shut down. Of course, we have two inverters
that do not shut down in that c