se.
>
>
>
> Thanks!
>
>
>
> William
>
>
>
>
>
>
>
> [image: Gradient Cap_mini]
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.or
Mason
Sent: Thursday, July 03, 2014 3:31 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 208 volt off-grid well pump
William,
If your voltage at the pump is 205 voltage at no load, it is not a cable issue,
your source of power is at too low a voltage. Voltage drop is proportional to
current, no c
Here's your buck boost:
http://www.acmetransformerspro.com/acmebuckboosttransformers.htm
On Thu, Jul 3, 2014 at 2:33 AM, William Miller
wrote:
> Friends:
>
>
>
> About two months ago I inquired of this forum about complications that
> might result from running a residence on a 208 volt 3 phase
William,
If your voltage at the pump is 205 voltage at no load, it is not a cable
issue, your source of power is at too low a voltage. Voltage drop is
proportional to current, no current, no voltage drop.
Most 208V system are run at about 215v, to allow for some drop and to
facilitate 240v equipmen
Friends:
About two months ago I inquired of this forum about complications that might
result from running a residence on a 208 volt 3 phase system. One
respondent indicated that motors might be affected. Sure enough the owner
is having problems with the well pump. It is tripping circuit brea