Best-
Mike
From: RE-wrenches On Behalf Of
Blake Gleason
Sent: Thursday, April 18, 2019 5:20 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 1000 volt
Bill,
Watch out for the 480 delta with the SMA inverter. Even though the product
literature says it works, it doesn't. If there's eve
Bill,
Watch out for the 480 delta with the SMA inverter. Even though the product
literature says it works, it doesn't. If there's ever a ground fault (PV
system or customer facility wiring) on one of the 480 legs, the other two
legs will jump to 480V to ground (with much higher spikes along the
Wrenches,
I'm tackling a huge residential system that requires
back-feeding the grid at 480 volts, delta (no neutral, right?). We're
going to GT 30-50 KW. The SMA SB3TL-US-10 is one of the few
inverters (apparently) that can do this, which I'm planning to use. The
inverter c
: Wednesday, May 18, 2016 1:33 PM
To: RE-wrenches
Subject: [RE-wrenches] 1000 volt wire for trench-buried extended runs - what
type?
HI Scot,
I”ve pretty cavalier on lots of things. But for this, I would use conduit and
wire.
I just think the added protection, being able to pull out wire in
HI Scot,
I”ve pretty cavalier on lots of things. But for this, I would use conduit and
wire.
I just think the added protection, being able to pull out wire in case etc.
I do like the armored cable that was discussed, but that stuff is expensive and
the ends are quite expensive.
I buy my
Behalf
Of James Rudolph
Sent: Monday, July 06, 2015 8:35 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] 1000-volt circuits
Aloha Marco,
Did you come up with any solutions to this problem? We may have a few here on
Oahu in development that may go this way as well.
Mahalo Nui Loa,
James B
Aloha Marco,
Did you come up with any solutions to this problem? We may have a few here
on Oahu in development that may go this way as well.
Mahalo Nui Loa,
*James B. Rudolph*
*Haleakala Solar*
*Director of Operations*
*NABCEP Certified PV Installer # 091209-155*
On Wed, Jul 1, 2015 at 9:01
Marco
Does not sound like you have the correct license, this is as per state of
Hawaii its all in the last line,
everything from wire connectors and boxes may need additional ratings as
well
Jerry
NABCEP 051112-169
C-63
High voltage electrical contractor
To place, install, erect, or connec
Hola amigos y amigas.
We're doing our first projects here on the Big Island of Hawaii using
1000-volt rated inverters.
The AHJ is informing us that those electricians working on these circuits
require training specific to working on 600+ volt circuits.
Anyone know of such training(s)?
...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander
Sent: Friday, May 16, 2014 1:43 PM
To: RE-wrenches
Subject: [RE-wrenches] 1000 volt conduit??
Hello,
Is there any specific conduit you'd recommend for 1000 volt arrays? I can't
find any
Hello,
Is there any specific conduit you'd recommend for 1000 volt arrays? I can't
find any reference of a voltage rating for EMT, ridged, PVC, etc. in the
code or spec sheets. Are these types OK to use? I assume its OK as long as
1000v rated wire is used. Am I correct? Thanks.
Kirk Herander