responders safety compared with rooftop shutdown at within 1' of the array
group. I have seen others on this list agree to as much and the test labs
basically validate this in my eyes.
From: Jason Szumlanski
To: "RE-wrenches"
Cc: Vincent Jolissaint
Subject: Re: [RE-wrenches]
(sorry sent the previous reply before it was complete)
Hi Jason,
Currently Tesla doesn't allow any totally off-grid installations with PW3
or PW3, they used to support this through the Gateway but no longer do.
In addition, the Powerwall 3 will require at least a single MCI per string
to pass the
Hi Jason,
Currently Tesla doesnt allow any totally off grid installations, they used
to support this through the GW2 but no longer do.
In addition, the Powerwall 3 will req
>From: Jason Szumlanski
>To: RE-wrenches
>Subject: [RE-wrenches] Powerwall 3
>Message-ID:
>
>Content-Type: text/p
Michael, it is super scary to hear these stories and they are a good
reminder that Li-ion technology still has risks. I am glad the manufacturer
is taking care of you, but it is concerning to see that the battery safety
systems allowed the thermal runaway event.
Hopefully, the fire department code
Hi all,
I bought a 80w CO2 laser cutter engraver from Ebay a few years ago and have
been running it each evening as a nice side business. It was about $2000 to
purchase. Ise 2 layer laser engraving plastic from Johnson Plastic with 3M
double side tape pre-applied.
I found out later that I really
Hi Jeff,
I prefer this panel for this need. it has a dedicated left side for
(2) @100A breakers max or (1) @ 200A max PV backfeed.
https://assets.new.siemens.com/siemens/assets/api/uuid:4e2c50f4-f20a-481c-8cb4-bd817cd7cb04/sie-fl-400srmetercombo.pdf
In addition, it has all the features of a typi
2021 International Fire Code
Revise as follows:
1207.11.7 Protection from impact. Stationary storage battery systems ESS
installed in a location
subject to vehicle damage in accordance with shall Section 1207.11.7.1 or
1207.11.7.2 shall be
provided with impact protection in accordance with Sectio
Hi Al,
One good CSED is the Square D SC3042M200PS. It has a factory line side tap
location available.
*With Regard,*
*Vince Jolissaint*
*Cobalt Power Systems Inc. |*
*Director of CAD Services*2557 Wyandotte St. | Mountain View CA 94043
Office: 650.938.9574 | E-Mail vince...@cobaltpower.com
O
Hi Kirk, the maximum actual charge rate is 5kW per Powerwall. When you
exceed that, or start getting full batteries, the Gateway tells the
Powerwalls to frequency shift to 62-66 Hz.
This takes the UL 1741 listed inverters out of the sweet spot, and they
stop or curtail production. However, predict