Re: [RE-wrenches] SolarEdge

2024-12-13 Thread Howard Scot Arey via RE-wrenches
What a swap over...we have a muni project where the higher voltage optimizers on the 480v inverter allowed us to minimize conductor sizing. New central inverter would need to support strings that use that size. And then the labor to remove all those optimizers! But we're replacing one of those inve

[RE-wrenches] Repetitive and unknown arc-fault codes with this combination...Sunpreme bi-facial and Fronius IG

2015-06-18 Thread Howard "Scot" Arey
uctor back to the Fronius 10.0 where we used the distribution plate to spead the amperage across the six string input channels. I'm stuck - any thoughts on other potential arc-fault causes? Howard "Scot" Arey 254-300-1228 scot.a...@sola

[RE-wrenches] Whole house solar backup using service entrance conductors from utility - transfer switch or stacked inverters to get 200amp through during normal grid ops?

2015-05-15 Thread Howard "Scot" Arey
er switch where both the grid and the backup position are open (still allows PV grid-tied operations to sell back to grid and partially offset loads during normal grid ops) but closes the grid connection during grid failures so that the battery backup provides power (with 2 Radians only). Howard

[RE-wrenches] 480 Wye or Delta for a SolarEdge 10K 3-phase; how can I determine what this panel is?

2014-12-15 Thread Howard "Scot" Arey
indicated above? - If the 4th wire is a neutral (I certainly hope it is), where might I find the ground electrode conductor (the building is relatively new, less than 10 years I believe.). FYI, the building is metal. I look forward to your comments Howard "Scot" Arey