I'm guessing it's an azimuth Wattsun, given that only one linear
actuator is visible, and the earlier tilt'n'roll had two. I sent William
a 2009 AZ-125 manual in pdf.
Allan
On 7/21/2020 8:37 PM, Dave Angelini Offgrid Solar wrote:
Not enough resolution to id. Best guess is pre AZ-125 which is
Not enough resolution to id. Best guess is pre AZ125 which is long gone.
Ask Jeff at Wattsun! --Dave
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail offgridso...@sti.net
text 209 813 0060
On Tue, 21 Jul 2020 14:46:57 -0700, William Miller
That's going to be long extension cord for most off grid projects...
Ray Walters
Remote Solar
303 505-8760
On 7/21/20 12:11 PM, Matt Partymiller wrote:
Jay,
The Tesla Gateway has a 12v input terminal for boot up. To startup my
off grid Powerwall we wired in a 12V power supply to the inp
Friends:
If anyone has a manual for this tracker, I would really be grateful to receive
it. Pretty sure it’s some form of Wattsun tracker.
TIA
William Miller
www.millersolar.com___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.
I'm not a fan of this strategy. What happens when the coil fails? It's not
a failsafe solution IMO.
Jason Szumlanski
On Tue, Jul 21, 2020 at 10:52 AM
wrote:
> Larry,
>
> Connect the coil of a 240 VAC contactor to the output of the generator
> circuit. Have the contacts of the relay break the
Whoever drew that up made it look like the generator is the common pole. I
know what they were getting at, but it's a pretty poor way of depicting it.
On Mon, Jul 20, 2020 at 6:15 PM la...@starlightsolar.com <
la...@starlightsolar.com> wrote:
> This, from a Nov 03, 2017 Powerwall 2 document, ma
Sorry - Automatic Generator Start.
What I'm wondering now is how does it manage PV inverter output and
generator power operating simultaneously? I think they are saying the
generator will not automatically start if there is PV inverter input output
present. If that is the case, what happens when t
Jay,
The Tesla Gateway has a 12v input terminal for boot up. To startup my off grid
Powerwall we wired in a 12V power supply to the input terminals and plugged the
other side into a grid-connected outlet. Some version of this is part of their
off grid process.
We’ve been running a reasonable
Connecting a generator output to the inverter output has the potential to
damage the generator control board.
Another way to go is to put a diode on the output of the generator and parallel
it into the DC input to the GT inverter. Preferably you’d want a larger
generator than the GT inverter.
Larry,
Connect the coil of a 240 VAC contactor to the output of the generator
circuit. Have the contacts of the relay break the AC coupled feed.
Drake
---
On 2020-07-20 16:25, William Miller wrote:
Larry:
If you can automate disabling grid-sell when connected to the generator in a fo