John,You did say that the Line tie LED was on so you must have it in Sell mode;OK.The INV/CHGR is likely in a Bulk charge mode(is the Bulk LED on?).Once the INV/CHGR has completed the Bulk charge then it will drop down to the Float charge mode(Float LED ON).Now that the INV/CHGHR is in the Float mo
Chris,
When I do this for a client, I add a second inverter/charger
and make a completely redundant system. This way it can be powered from the
DC bus or AC trickle charged which is very easy to automate.
Dave Angelini
Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgrid
I don't think I quite see the advantage of that plan. The HUPs do not
die with quick catastrophic failures like L16s often do. They usually
just slowly lose a little capacity each year, begin to use a bit more
water, and become a bit less efficient in charging. How old are the
HUPs and what a
Dear people:
I have a customer with a solar array for his 24V system, Bergey Excel 10
wind genny, 12KW Kohler generator, two Outback controllers and two FX
inverters. He currently has a set of the Solar One SO-6-100-33/24
batteries, which have maybe a year or two left in their life. What he wou
What's the error on the controller
On Mon, Nov 12, 2018, 00:49 John Blittersdorf Hello Wrenches,
>I have a customer with a Generac EcoGen 6kw that starts and runs for
> about 30 seconds and then shuts down with high engine temp error. The
> engine is stone cold so it must be a temp sensor fai
Also don't forget to set the (18) Grid Usage Timer
Christopher
On Mon, Nov 12, 2018 at 1:35 AM, wrote:
> and the yellow "line tie" led should be on.
>
>
>
> todd
>
>
>
>
>
>
>
> On Sunday, November 11, 2018 9:30pm, "Ray" said:
>
> I'm sure you did this, but did you set menu 9 (Inverter Setup)