Hi Jay,
Is this for an inverted output circuit? If so then I think the NEC reference
you’re looking for is 705.95(B). That says you can size the neutral to the
same size as the EGC if the neutral is used only for instrumentation, voltage
detection or phase detection.
A number of single phase
Here is the code reference explaining this conductor size disparity from 2017
NEC:
"According to Table 310.15(B)(16), a 3/0 AWG, Type THW copper conductor
has an ampacity of 200 amperes. However, for a 3-wire, single-phase
dwelling unit service, as shown in Exhibit 215.2, 310.15(B)(7) permits a
s
Hi Wrenches,
I've got a proposal out there for about a 11.5 kW grid-tied system. We are
planning on using Enphase IQ 7+ inverters. Quick question, this guy has a
pretty large Ham Radio setup operating at 3-30 MHz. He has a directional
antennae that can push 1500W sometimes. Has anyone had any
What about 4/04/02/0 aluminum, service feed? Or is that utility excepted?
Dana Orzel Great Solar Works, Inc.
C - 208.721.7003 d...@solarwork.com
Idaho Contractor - # 028
At the risk of sounding like a grandpa Wrench...I've never had or seen a
neutral conductor be smaller than current carrying.
marco
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Jay
Sent: Friday, September 21, 2018 3:47 PM
To: re-wre
There definitely areNEC signage requirements. VT is in NEC 2017. I'll
put the references below each bullet.
On 9/21/2018 2:55 PM, David Palumbo wrote:
What is the current code requirements around the country for required
signage for a residence/business with back-up battery storage?