Re: [RE-wrenches] Sunny Island no Longer Supports TLs - How about New Series?

2017-03-26 Thread b...@midnitesolar.com
Battery based rapid shut down is not simple. Much of it is up to the AHJ. You can shut down the AC output or the battery or both. Shunt trip battery breakers do not cost much more than regular battery breakers. You do need to control them though. That is what the Birdhouse and MNbattery disc

Re: [RE-wrenches] Sunny Island no Longer Supports TLs - How about New Series?

2017-03-26 Thread Ray
First, its the added cost of the disconnecting combiner, RT breakers, control boards, Main initiator, and extra labor for wiring and testing. I'd say it ads another $2 to $3K of cost. Not a big deal on large systems but for a smaller off grid project in the $10K range, its a huge increase in c

Re: [RE-wrenches] Sunny Island no Longer Supports TLs - How about New Series?

2017-03-26 Thread Drake
Jeff, I just went through this. The SI and the US 40s still work together. They do not use a 485 card. The Sunny Boys are programmed in off grid mode, and the Sunny Islands take care of the UL1741 requirements. Tim at SMA gave me this information. The Sunny Boys will taper charge as shown on

Re: [RE-wrenches] Sunny Island no Longer Supports TLs - How about New Series?

2017-03-26 Thread Dan Fink
Hello Ray -- Can you elaborate on why these battery-based projects are getting killed here locally? Is it the misinterpretation by AHJs that 690.12 has to disconnect the inverter from the battery bank with giant shunt-trip breakers? If that were the case...backup generators would have to be control