[RE-wrenches] LG neon 365 watt 72 cell modules, who sells them

2016-03-02 Thread Steven Lawrence
We can get these modules straight from LG, so they are available in the US. Did you try LG to get a list of distributors they send to? ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email addres

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread billbrooks7
All, Here is the new language that has been approved for the 2017 NEC (more authoritative than JW). 705.12(B)(3)(d) (d) A connection at either end, but not both ends, of a center-fed panelboard in dwellings shall be permitted where the sum of 125 percent of the power source(s) output

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread Glenn Burt
I believe that John Wiles has stated this in a couple of places in print, therefore you may have a tough time justifying a way around the rule to an AHJ. Supply side connections are very popular in this situation. -Original Message- From: "August Goers" Sent: ‎3/‎2/‎2016 11:32 To: "RE-w

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread William Miller
August: Our AHJs are correctly treating the top or bottom most breaker positions as "the opposite end." As you examine the problem you realize the only scenario in which currents add is if load breakers are NOT between the main and PV feeders. Locating PV feeders at either end of the bus acco

Re: [RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread frenergy
Fortunately we haven't had that AHJ 'problem'. It probably wouldn't work (in the mind of your AHJ) to move the heavy loads to one side and install your backfed breaker on the far end of the 'lighter' side of the center tap. I know I'm probably dreaming. It seems the 2 buses must be desi

[RE-wrenches] NEC 705.12 Point of Connection - 120% rule for center-fed panelboards

2016-03-02 Thread August Goers
All – We are seeing more AHJs not allowing us to use the NEC 7015.12(D)(2)(3)(b) 120% rule on center-fed panelboards. For example, if we have a 100 A meter/main combo with a center fed 100 A breaker we cannot apply the 120% rule at all and need to do a panel swap. What are other wrenches doing i

Re: [RE-wrenches] LG neon 365 watt 72 cell modules, who sells them?

2016-03-02 Thread Peter Parrish
You might try Borrego Solar. Peter T. Parrish, Ph.D. President, SolarGnosis 1107 Fair Oaks Ave. Suite 351 South Pasadena, CA 91030 (323) 839-6108 peter...@pobox.com From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Daniel Tittmann Sent: Tuesday, March