I'd recommend going to usplastic.com and looking at their high density
polyethylene rectangular tanks. I think the brand is Tamco. They come in a
variety of sizes. They are sturdy 1/4" poly. You can get fitted lids. It's easy
to hole saw them for conduit. I have used them a few times for small b
Living off grid, I have found "drop" to be useful for time's (at night) when
using small generator (6.5kw) to assist with the batteries but we want to run
the microwave for a few minutes which can bog down the generator. Yes flipping
the breaker will do the same thing. But breakers don't auto re
Hi Chris,
Can the GSMM be used with non Generac generators?
Howie Michaelson
NABCEP Certified Solar PV Installer™
Sun Catcher
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004
On Feb 5, 2016 3:17 PM, "Chris Mason" wrote:
> Sorry, autocorrect. A Generac
Drop Mode is handy for Grid Tied Systems to cycle the batteries. Just engage drop mode, the system sees the grid but does not lock on and the system runs off renewables till the batteries need charging. As long as the system "sees" the grid, it will lock on before it crashes. TTFN dbDan BrownFoxfir
Supply side connection.
-Original Message-
From: "Daniel Tittmann"
Sent: 2/5/2016 13:33
To: "RE-wrenches"
Subject: [RE-wrenches] grid tied systems with seperate generator back up
Esteemed colleagues-
We are finding more and more clients with existing utility back up
generators that
A general smart management module will sense the generator is running and
disconnect the inverter. No wires required.
On Feb 5, 2016 14:33, "Daniel Tittmann" wrote:
> Esteemed colleagues-
>
> We are finding more and more clients with existing utility back up
> generators that are wanting grid in
Sorry, autocorrect. A Generac smart management module.
On Feb 5, 2016 15:34, "Chris Mason" wrote:
> A general smart management module will sense the generator is running and
> disconnect the inverter. No wires required.
> On Feb 5, 2016 14:33, "Daniel Tittmann" wrote:
>
>> Esteemed colleagues-
Hi Daniel,
Ive done this with 4- 5048 sunny islands. 2 per phase
generac smart switch service entrance rated transfer switch.
no critical load panel, output of islands feeds main panel, (100a)
On grid loss, Transfer switch opens, Islands take over from batteries/solar.
Aux relay in master sunny isl
William,
I know there was a point that they changed processors, when they did that it
made the power assembly, control assembly, and the ac assembly incompatible.
I agree with you that it would have been nice that they could have maintained
this, but this change was quite some time ago, at le
Wrenches
My best solution is connect the pv unstream of the tranfer switch, if that
is not an option install a contactor in the pv AC side output and connect
that upstream of the genny, you can also connect the supply power to the
genny side. Either way you look at dont let the PV and genny play to
Power wall?
> On Feb 5, 2016, at 7:31 AM, Jay wrote:
>
> Hi all
>
> I have a customer who has an old outback PS1-be. ( long extinct)
> Battery enclosure that holds 4 group 27 12v batteries.
>
> Anybody know of anything similar? He wants to add but I can't find anything
> in a similar shape
Not too hard to build with Unistrut and skin with plywood.
-Original Message-
From: "Jay"
Sent: 2/5/2016 10:31
To: "RE-wrenches"
Subject: [RE-wrenches] Battery enclosures
Hi all
I have a customer who has an old outback PS1-be. ( long extinct)
Battery enclosure that holds 4 group 27
Esteemed colleagues-
We are finding more and more clients with existing utility back up
generators that are wanting grid inter tied solar systems. Many of these
clients are not willing to go the extra mile to interface the solar system
with the back up gen. I am wondering if any of you out there
Hi all
I have a customer who has an old outback PS1-be. ( long extinct)
Battery enclosure that holds 4 group 27 12v batteries.
Anybody know of anything similar? He wants to add but I can't find anything in
a similar shape. I.e. Tall and narrow.
Any suggestions?
Thanks
Jay
Peltz power.
Sketchip with Skelion plugin.
On Feb 4, 2016 20:16, "Allen Frishman" wrote:
> Hey Wrenchers,
> Anyone know of a good software tool that provides estimated performance
> data for a solar array on a New Construction building that has not yet been
> built? Specifically looking for a user friendly