Is the other side of the coin, though, use one string of high capacity L-16's
to: reduce the number of cables and their connections to terminals (failure
points, maintenance), reduce the watering hassle (half as many cells to check,
water, take SGs), because there are less cells you're more like
Thanks, esteemed Wrenches,
I'm thinking that she would do fine with 440 A/hr of T105 REs. Jay
asked about her loads. I emailed her this earlier today:
Beverly,
Back when the batteries were still strong, if you ended a day's
charging at 100%, what would the pe
Carl
They look like the Westinghouse product. Their new name is Andalay solar ( no
Seinfeld reference ). We installed one of these, very high failure rate with
the enphase 190's requiring us to remove the system and replace them. All the
splice rods where corroded and we had to use a sawzall
Dan,
That's right about the unprotected DC + main. Trace used the
inverter GJ, so turning off DC loads required turning off the DC to
the inverter - which meant reprogramming it afterward. And it used a
#10 tap pigtail. Stoopid.
If I have several DC loads I have
Look at HDPE. It is a fused pipe, very tough, flexible, available in a
variety of wall thicknesses.
On Fri, Oct 23, 2015 at 3:52 PM, Kirk Herander wrote:
> Hello,
>
> I’m replacing an old Solarjack pump with a similar Sunpump in a tiled well
> about 12’ deep. I’d like to find a flexible water pi
Kirk,
This is on my iPhone and I'm barely literate on it compared to my kids, so
it'll likely mess up...
Use 3/4" SDR-9 black 140 psi black poly pipe with sleeved compression
connectors. This has been used for years for hand installation of submersibles,
down to 250-350'. I would guess that it
Hello,
I'm replacing an old Solarjack pump with a similar Sunpump in a tiled well
about 12' deep. I'd like to find a flexible water pipe so I can leave enough
coiled in the well to pull the pump straight out to dry land without
disconnecting. Standard poly pipe kinks too easy. Thanks.
Kirk He
The YC1000 is only three phase.
On Fri, Oct 23, 2015 at 1:01 PM, Benn Kilburn
wrote:
> APS microinverters will work. Each YC500A handles two modules each and
> each YC1000 handles 4 modules.
>
> https://usa.apsystems.com/
>
> *Benn Kilburn *
> CSA Certified Solar Photovoltaic Systems Electrician
Thanks, everyone. I see I'm not the only one juggling competing concerns
on the battery fuse issue. For the service call that motivated my query
I think we'll leave it as is - the installation has short battery cables
in conduit into an Outback system, and no easy way to mount a fuse
external t
Thanks, but this is residential. 120/240
J
Sent from my iPhone
> On Oct 23, 2015, at 10:02 AM, Jerry Shafer wrote:
>
> The enphase 250 if you had 3 phase might try a SMA 3K-22
> Jerry
>
>> On Oct 23, 2015 6:39 AM, "jay" wrote:
>> HI All,
>>
>> What is the recommendation for 72 cell 280 watt
The enphase 250 if you had 3 phase might try a SMA 3K-22
Jerry
On Oct 23, 2015 6:39 AM, "jay" wrote:
> HI All,
>
> What is the recommendation for 72 cell 280 watt 120/240v micro inverters?
>
> Enphase don’t have one.
>
> This is on my old house. Still has a AEI-GC-1000.
> The modules have got t
Dave, it's 6 T-105s and over the winter the only load is the CC and
inverter. Temperature is unknown, though likely gets to -20F. There is
insulation, not that it does any good if they are not charging to capture
some heat.
Dan Fink
Adjunct Professor, Ecotech Institute
IREC Certified Instructor™ f
APS microinverters will work. Each YC500A handles two modules each and each
YC1000 handles 4 modules.
https://usa.apsystems.com/
*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
6706 – 82 Ave NW | Edmonton, AB | T6B 0E7
P: 780-474-8992 | F: 888-405-5843 | w
HI Dan,
All the big three have the same wiring diagrams with a positive buss and then
breakers going out from there.
And yes there is no main disco for the DC branches.
But if your point was that the fuse could/will blow and then you have the
PV/wind connected to the inverter and could ove
Hi Allan and Jay,
I second the golf cart battery option. Trojan T-105s seem to be the
most bang for the buck. An 800 W array wouldn't stir up the
electrolyte sufficiently in an L-16. Maybe the backup generator
would. What all is she running?
Drake
At 06:40 PM 10/22/2015, you wrote:
Hi Al
HI All,
What is the recommendation for 72 cell 280 watt 120/240v micro inverters?
Enphase don’t have one.
This is on my old house. Still has a AEI-GC-1000.
The modules have got to come off as well as they are old mobil’s.
All just about dead.
I’ve got a good deal on 72cell, 280 watt modules,
wolfgang.beaugr...@magesolar.com
Kurt Johnsen
On Thu, Oct 22, 2015 at 8:52 PM, Carl Adams wrote:
> Hello Fellow wrenches,
>
> I have a couple of failed Mage solar AC modules. These are Mage Solar
> panels with an integrated Solardridge inverter. Anyone have a good contact
> number for Mage So
Hey Dan,
Interesting voltage numbers. How many T-105's in this system and what is the
load? What is the temperature of the battery bank?
Thanks,
Dave
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Dan Fink
Sent: Friday, October 23, 2015 10:51 AM
To:
Esteemed Wrenches;
This creeps me out too and sometimes causes lack of sleep.
The Midnite Solar power panel install manual shows no OCPD on in DC + main
from battery bank to power panel. Easy to wire the main DC breaker to
control those conductors, but then you have a "self destruct" switch if
syst
Thanks guys for the recommendations.
-Dave
*--*
*Dave Tedeyan*
*Project Engineer*
*Taitem Engineering, PC*
109 S. Albany Street, Ithaca, NY 14850
Voice: (607) 277-1118 x121
www.taitem.com
On Wed, Oct 21, 2015 at 6:38 PM, Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:
> I recent
It's ALWAYS good practice to install a current limiting fuse at the battery
bank, if fact it's very poor practice not to. We're working with a lot of
larger lithium ion phosphate manganese systems and I would not install them
without it. As far as working on someone else's install, make your co
At an absolute minimum a current limiting the fuse at the battery bank is
required if not by the law by common sense
In banks with multiple strings in the past I have fused each string
I have seen banks in the past where a single battery failed and for lack of a
better description the others gan