Hello Wayne,
Seems to me like the AHJ is asking for the bus bar rating of the main load
center which is usually printed on a sticker inside the panel (only visible
with the dead front removed).
Then he also wants the rating of the main breaker that is installed to protect
the panel (read right o
We're still not at the bottom of it. Seems Mitsubishi is doing their level best to finger the RE system. Yes, the current wave form (On a Fluke 43 Power Analyzer) has a shoulder.. looks down right funky on one inverter thru the X240 until the 2nd inverter lights. Current also looks funkular when ea
As a rull we will only use panel rating 200 is 200 not labeled is in
question
Jerry
On Nov 30, 2014 1:45 PM, "Wayne Irwin" wrote:
> Hello Wrenches,
>
> Hope you all had a nice Thanksgiving.
>
> I have an AHJ asking for the service panel buss rating and the service
> panel buss protection rating.
Hello Wrenches,
Hope you all had a nice Thanksgiving.
I have an AHJ asking for the service panel buss rating and the service panel
buss protection rating.
Am I correct to assume that the rating is the service panels designated rating
x 1.2% (ie 200A x 1.2 = 240)?
and that the buss protection
Greetings.
I'm looking for two SMA HF inverters (2, 2.5 or 3 kW), new or used, but
gotta be working properly.
Please contact me off-list.
Thanks,
marco