[RE-wrenches] Permanently installed power monitoring equipment

2014-08-27 Thread William Miller
Friends: I am considering the option of installing power quality monitoring equipment at a facility. The system is three phase 120/208 Wye. I need to monitor for voltage, frequency, sags, dips and flicker. Can anyone recommend anything that can do this? Thanks in advance. William

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Dan Fink
Hi Mac, all; Since Colorado just adopted NEC2014 July 1, I have not heard any AHJ stories yet. But look at 690.12 (1): "Requirements for controlled conductors shall apply only to PV system conductors of more than 5 ft in length inside a building, OR more than 10 ft from a PV array." (my emphasis on

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Brian Mehalic
Hey Mac, 1. What is a (currently listed) rapid shutdown system that will accommodate 8 strings? I know I can do this with Midnite combiners but as I understand these aren't listed yet. Contacting combiners from several mfgs or Midnite combiners would work. Everything in PV systems pretty mu

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Will White
That’s correct it’s a manual disconnect and I agree it totally defeats the purpose but some AHJ’s are accepting that it’s within 5’ of entering the building and nowhere in the code does it say it has to be readily accessible. We had one AHJ make us put the disconnect on the side of the house abo

Re: [RE-wrenches] inverter monitoring

2014-08-27 Thread August Goers
Hi Don, You might want to check with your distributors to see if they have the old Power-One equivalent to the VSN700 data logger. I know that these are available because I just bought one for a new project. The PN is VS701 – N0 (called Aurora Logger). We’ve installed a few of these with good re

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Mac Lewis
Hi Will, Yes I'm sure AHJ's will be all over the place for a while here in Colorado. To clarify, is this a manual disconnect in the attic? If so, that is really missing the whole idea of a rapid shutdown. Thanks On Wed, Aug 27, 2014 at 7:47 AM, Will White wrote: > Our experience in MA with

Re: [RE-wrenches] Inverters Maximum Input Ratings

2014-08-27 Thread Nathan Charles
I wrote an open source library called solpy to explore some of these issues. https://github.com/nrcharles/solpy It's not user friendly but you can watch the DC power available at the array. It implements the CEC inverter model and when I matched it up with Enphase's 5-minute data it tracked fairly

Re: [RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Will White
Our experience in MA with rapid shutdown unfortunately varies with AHJ. Some are letting us put an Eaton NEMA 4 disconnect on the roof next to the array. Some are letting us put a disconnect in an accessible attic within 5’ of the penetration. Some are requiring the Midnight Birdhouse remote

[RE-wrenches] Rapid shutdown questions

2014-08-27 Thread Mac Lewis
Hello wrenches, I am still trying to wrap my head around how to comply with rapid shutdown in off-grid and hybrid situations. I've got a few questions that maybe you can help with. 1. What is a (currently listed) rapid shutdown system that will accommodate 8 strings? I know I can do this with

Re: [RE-wrenches] Inverters Maximum Input Ratings

2014-08-27 Thread Matt Partymiller
Rebekah, My understanding was that PVsyst modeled inverter nominal power not maximum power. I believe this helps to compensate for inverter temperature limitations. For instance, depending on inverter location and power ratio, I would suppose that there may be instances where the simulation coul