To at least partially answer Ray's question about Class-R fuses: Square-D
Heavy Duty fused disconnects, commonly used as DC discos for PV arrays and
which use Class-R fuses, are only rated for 80% duty. The non-fused HD
discos are 100% rated in PV systems. I'm not sure if that is because of
the fus
Fan kits through Sharp are no longer available and it is tough to find ones
that work
On Aug 22, 2014 4:49 PM, "William Miller" wrote:
> Friends:
>
>
>
> I have a new client with some very old inverters. I know nothing about
> the Sharp inverters. This person is on a fixed income and I am trying
I have a service manual, doesn't say much but if you need it let me know
Thanks,
Joe Pizur
Alternative Energy Solutions
1.775.857.1157 1.775.233.3290 (cell)
alternativeenergysoluti...@msn.com
Nevada License # 57117/RPV-906
NABCEP Certified InstallerNABCEP Certified Technical Sales
From: w
Joe:
Perfect. Thanks!
William
Miller Solar
> On Aug 22, 2014, at 6:39 PM, aes Alternative Energy Solutions
> wrote:
>
> According to the service manual I have;
>
> d-29 = "Fan Lock"
> Cause: fan is locked
> Cause: fan has failed
> Action: Replace
> Fan part#: 95KPZZ1036ZZ
>
>
>
> Thank
According to the service manual I have;
d-29 = "Fan Lock"
Cause: fan is locked
Cause: fan has failed
Action: Replace
Fan part#: 95KPZZ1036ZZ
Thanks,
Joe Pizur
Alternative Energy Solutions
1.775.857.1157 1.775.233.3290 (cell)
alternativeenergysoluti...@msn.com
Nevada License # 57117/RPV-90
Most combiner boxes, DC rated breakers, and DC rated fuses and fuse
holders we use today, qualify as assemblies for the 100% exception
(Outback, Midnite, etc.) so you only have to size the OCP by 125% of
short circuit current rating for edge of cloud effects.
Since the conductor is sized bas
Thanks Chris,
It's one of those great things about the solar industry that there is
always more stuff going on than one man can keep track of:
http://www.bentek.com/solar-products/recombiners/circuit-breaker/
> Mark,
> The term "recombiner" to me is an electrical panel used on the AC output
>
Friends:
I have a new client with some very old inverters. I know nothing about the
Sharp inverters. This person is on a fixed income and I am trying to help
her out on the cheap.
I read a D-29 error. My research indicates this is a fan error. Is this
correct?
Can this be repaired in
Mark,
The term "recombiner" to me is an electrical panel used on the AC output of
multiple inverters to combine their electrical outputs.
That is different to a "combiner" which connects solar strings through
fuses to a busbar for connection to the inverter using one conductor pair.
In grid tied s
Folks,
In looking at a circuit breaker based re-combiner for the first time, I am
now pondering the meaning of the Exception below:
NEC 2014 690.8 (B) Conductor Ampacity. PV system currents shall be
considered to be continuous. Circuit conductors shall be
sized to carry not less than the larger o
From the who-could-have-seen-this-coming department:
SolarWorld Recalls Solar Systems with Copper Grounding Lugs Due to
Electrocution, Electric Shock or Fire Hazard
SolarWorld solar panels installed with bare-copper grounding lugs can
corrode which could result in a faulty ground circuit, pos