Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-09 Thread Ray Walters
HI Chris; Just to be clear, the cables are not going to fail just because they aren't code compliant; unless you meant they would fail an inspection. I've included a picture of my own service rated at 150 amps. Using table 310.15(B)7 (which I believe is the correct table for sizing the serv

Re: [RE-wrenches] Conductor Sizing for Supply Side Connection

2013-03-09 Thread Christopher Warfel
Had a couple of minutes here, so with the load side connection, the 200 amp breaker would operate to protect all conductors. With a supply side connection, the battery charger could be pulling 60 amps, the main panel 200, and the service conductors sized for 240 amps would fail. 2/0 in free air