Re: [RE-wrenches] NEC 690.9 and Two String Arrays

2011-02-21 Thread Christopher Warfel
I'd like to suggest that Appendix J of John Wiles Suggested Practices Photovoltaic Power Systems and the NEC be read. It provides good instruction on how to calculate when an OCPD is needed. It is a function of the module's Isc rating, the inverter's backfeed current capabilty, and the module's

Re: [RE-wrenches] NEC 690.9 and Two String Arrays

2011-02-21 Thread Phil Schneider
Dan, My understanding has been that unless the inverter spec lists a "0 A backfeed current" then it is conceivable that fault current from the grid (up to the inverter OCPD) could feed a fault on the DC side, so DC fusing would be necessary (Fronius IG Plus spec sheet, for example, states this). S

[RE-wrenches] NEC 690.9 and Two String Arrays

2011-02-21 Thread dan
Hey Everybody.. I got the impression that 690.9 ex. allows up to two parallel strings to be connected (thru a disconnect) to a grid interactive inverter (which does provide Ground Fault Protection).. Do I still need to protect the Array from possible inverter back feed? This particular array consis

Re: [RE-wrenches] xantrex 600v controller

2011-02-21 Thread Jeff Oldham
It is still "vaporware" at this point. Rumors of a release 2nd or 3rd Q of this year. We'll see.Midnite Solar Classic 250's are starting to ship now as are the Apollo HV80's. From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative SOLutions _

Re: [RE-wrenches] Array tilt angle doesn't matter?

2011-02-21 Thread Bob-O Schultze
Jim, Obviously, your latitude will make a big difference. The further north you go the wider the summer to winter sun angle. Also, I'd want to know if that data was taken using just I/V curves or through a controller which had MPPT capabilities. In a real world situation with MPPT, I'm guessing