Re: [RE-wrenches] PENTAMETRIC

2010-01-08 Thread frenergy
Don, Seems the benefit of using % charge would go out the window if your batteries were sulphatedjust when you would need the voltage based/temp comp logic the most. No experience with your proposal though. Bill Feather River Solar Electric - Original Message - From:

Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread boB Gudgel
swingjun...@gmail.com wrote: Thanks to all who responded, The article Marco references, is the one referenced in the tinyurl in my original post. I did not find anything of significance in the previous Solar Pro issues. Based on the responses it seems there is no good data out there to answer

Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread swingjunkie
Thanks to all who responded, The article Marco references, is the one referenced in the tinyurl in my original post. I did not find anything of significance in the previous Solar Pro issues. Based on the responses it seems there is no good data out there to answer the question posted. This

Re: [RE-wrenches] Xantrex XW4548 noise problem

2010-01-08 Thread penobscotsolar
Hi Ryan, We have a lot of XW's installed and not one of them is what I would call loud. I would call the SW and SW Plus series loud. If it is simply that he is sensitive to noise I would recommend having a dead air space between whatever you layer the wall with. I built a recording studio for so

[RE-wrenches] Xantrex XW4548 noise problem

2010-01-08 Thread ryan
I have a customer that we installed a Xantrex XW4548 on a Midnite Epanel. He has 3kw of pv and 400ah of lead acid battery's. The issue is he feels the inverter is to noisy. The inverter is hung in a garage on a plywood wall that is 2 by 6 constructed with fiberglass and then drywall on the hous

Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread Kent Osterberg
Marco, Three components of power delivered by the utility company: Watts, volt-amps-reactive (VAR), and apparent power or volt-amps (VA).  Power factor is the ratio of the watts to the volt-amps.  PF = Watts/VA. To see how this works: draw a right triangle with 8 kW as the horizontal leg, 6 k

Re: [RE-wrenches] To Megger or not to Megger

2010-01-08 Thread wes kennedy
Hi Bill, I wanted to follow up on your results finding a ground fault with a lower resolution megger.     Do you think the .1MOhm meters will work in field applications? Do you know of any .001MOhm meters like the old 1520? I have taken a  position with a cadtel mfgr as their field applicati

Re: [RE-wrenches] Best angle - direct grid tie

2010-01-08 Thread David Brearley
Great format for an integrator and its staff. Thanks for sharing, Mike. David Brearley, Senior Technical Editor SolarPro magazine NABCEP Certified PV Installer  david.brear...@solarprofessional.com On 1/7/10 1:26 PM, "Michael Kelly" wrote: > Drake, >   > I did an analysis for optimum conditio

[RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread Marco Mangelsdorf
According to an article, written by a utility engineer on O'ahu, PF can be worsened at the site where a substantial PV system is located. If there is a poor or wavering PF due to an abundance of inductive loads at a particular site, having a large inverter, in relation to the overall power consump

Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread Joel Davidson
We worked on dozens of commercial PV systems in Southern California Edison (SCE), Los Angeles Department of Water & Power (LADWP), and San Diego Gas & Electric (SDG&E) territories. We installed Xantrex, SMA, and SatCon inverters and measured power factor on both the grid and the inverters. In e

[RE-wrenches] PENTAMETRIC

2010-01-08 Thread i2p
Input appreciated. How well does the Pentametric work as a generator control. The spec sheet states a control relay based on % charged is available. Any experience using the Pentamatic as a gen start control. Does this yield better battery control than voltage based approach? Thanks for any