I'm having a problem with an Outback VFX3524 inverter installed on an
E-panel in a remote off-grid location. Voltage at the inverter input
terminals is fluctuating between 110 & 140+ volts continuously. AC in
will not connect so batteries can't charge. Output voltage measured
at the inverte
Yes we can. I didn't know that the Aurora product had two separate MPPT
circuits. Thanks, I'll look into it.
- Peter
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779,
Can't you use an inverter with two separate MPPT circuits - ie. Aurora?
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Friday, December 26, 2008 2:30 PM
To: 'RE-wrenches'
Subject: Re: [R
I was afraid that the ultimate resolution would be another software cost
item. I'll look into PVSYST, and consider purchasing it if it is a
professionally-developed and maintained product, with pre-and post-sales
technical support, a policy of regular upgrades, runs on PCs and MACs, and
has a model
Peter and Darryl,
The right way to do this is using a computer program PVSYST ($800). It will
calculate the operating voltage of each string and the overall performance.
Not much else out there can calculate it. That being said, the loss of these
two orientations will be less than 2% based on the
5 matches