Re: [RE-wrenches] offgrid system question

2008-08-18 Thread jay peltz
Hi PHIL, Although the batteries may indeed be bad, I would point out that the the AC unit is turning on probably when the sun is out, therefore the total load isn't all on the batteries. And do we know they are XW inverters? thanks, jay peltz power On Aug 18, 2008, at 3:18 PM, Phil Unde

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread Phil Undercuffler
My .02 would be a close examination of the batteries, and a realistic realignment of their expectations of their capacity. 12 sun extender sealed AGM batteries, 305 AH at 12 vdc, wired for 915 AH at 48 volt DC -- sounds like those are the PVX-2580. They're only rated 305AH at the 120 hour rate.

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread tump
My sanyo mini split is a 36K btu unit/ 3 evaporators. My small gridtie system spins the meter backwards when unit is on full blast while suporting all the other house hold loads. AHH works sweet! Sent via BlackBerry by AT&T -Original Message- From: "Geoff Greenfield" <[EMAIL PROTECTE

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread Geoff Greenfield
I love my Mitsubishi "Mr. Slim" split system AC unit. I have a 9kbtu and a 15kbtu unit that share the same compressor. I have had both units come on at the same time while fridge, dishwasher, (gas) clothes dryer and staber washing machine all running, on top of "regular" loads. All this off of a

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread robert ellison
You don't list what the inverter is, but you might find that the battery voltage is dropping like lead when when the AC starts. If the system always started he AC look to the batteries, not good choice IMHO Another thing is, systems tend to grow with time and out grow the systems intended loads. H

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread Best Power Mario
Max, Let us know if the AC unit is 120 or 240Vac, what inverter/s are used, and how they are stacked. Mario Monesterio Best Power Intl. - Original Message - From: Max Balchowsky To: RE-wrenches Sent: Monday, August 18, 2008 3:00 PM Subject: Re: [RE-wrenches] offgrid system q

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread mick abraham
Max wrote about the "problem child" system which is "tripping off when the AC unit tries to start". Mick says: you didn't mention what brand of inverter is on board the system, but in any case there's probably an error code that you can find to explain the shutdown. The error could be due to th

Re: [RE-wrenches] offgrid system question

2008-08-18 Thread Max Balchowsky
Dear wrenches, going to look at a system installed by others and would like some input from some of you with more off grid experience than I have ( 4 systems over the years). the system was put on a new home - off grid 20 sharp ND123UJF panels 4 modules in series - 5 parrallel strings, 246

[RE-wrenches] SWCB cover needed

2008-08-18 Thread Allan Sindelar
Wrenches, I recently rebuilt an old and funky offgrid system into Safe'n'Good. The inverter was a Trace SW4024 (with Rev. 1.0 chips, which we upgraded to Rev. 4.01) with no DC disconnect. We added a used Trace DC conduit box to enclose the inverter cables. Somehow I haven't been able to find the DC