Hi PHIL,
Although the batteries may indeed be bad, I would point out that the
the AC unit is turning on probably when the sun is out, therefore the
total load isn't all on the batteries.
And do we know they are XW inverters?
thanks,
jay
peltz power
On Aug 18, 2008, at 3:18 PM, Phil Unde
My .02 would be a close examination of the batteries, and a realistic
realignment of their expectations of their capacity. 12 sun extender
sealed AGM batteries, 305 AH at 12 vdc, wired for 915 AH at 48 volt DC
-- sounds like those are the PVX-2580. They're only rated 305AH at the
120 hour rate.
My sanyo mini split is a 36K btu unit/ 3 evaporators. My small gridtie system
spins the meter backwards when unit is on full blast while suporting all the
other house hold loads. AHH works sweet!
Sent via BlackBerry by AT&T
-Original Message-
From: "Geoff Greenfield" <[EMAIL PROTECTE
I love my Mitsubishi "Mr. Slim" split system AC unit. I have a 9kbtu and a
15kbtu unit that share the same compressor. I have had both units come on
at the same time while fridge, dishwasher, (gas) clothes dryer and staber
washing machine all running, on top of "regular" loads. All this off of a
You don't list what the inverter is, but you might find that the battery
voltage is dropping like lead when when the AC starts. If the system always
started he AC look to the batteries, not good choice IMHO
Another thing is, systems tend to grow with time and out grow the systems
intended loads.
H
Max, Let us know if the AC unit is 120 or 240Vac, what inverter/s are used,
and how they are stacked.
Mario Monesterio
Best Power Intl.
- Original Message -
From: Max Balchowsky
To: RE-wrenches
Sent: Monday, August 18, 2008 3:00 PM
Subject: Re: [RE-wrenches] offgrid system q
Max wrote about the "problem child" system which is "tripping off when the AC
unit tries to start".
Mick says: you didn't mention what brand of inverter is on board the system,
but in any case there's probably an error code that you can find to explain the
shutdown. The error could be due to th
Dear wrenches, going to look at a system installed by others and would like
some input from some of you with more off grid experience than I have ( 4
systems over the years). the system was put on a new home - off grid 20 sharp
ND123UJF panels 4 modules in series - 5 parrallel strings, 246
Wrenches,
I recently rebuilt an old and funky offgrid system into Safe'n'Good. The
inverter was a Trace SW4024 (with Rev. 1.0 chips, which we upgraded to Rev.
4.01) with no DC disconnect. We added a used Trace DC conduit box to enclose
the inverter cables. Somehow I haven't been able to find the DC