Hi Bill,
Can you explain why the 6kVA rule on split phase systems?
I mean why 6?
thanks,
jay
peltz power
On Aug 8, 2008, at 8:48 PM, Bill Brooks wrote:
Jeff and Ryan,
The 6kVA value comes from the California Rule 21 that I worked on.
It only
applies to split-phase 240V systems (6kVA on 1
Jeff and Ryan,
The 6kVA value comes from the California Rule 21 that I worked on. It only
applies to split-phase 240V systems (6kVA on 120V). There is no specific
limit for imbalance on a 3-phase service.
A basic rule for single phase generation on a 3=phase service is to rotate
among the phases
Yes. contributions to Redwood Alliance qualify for tax deductions. Also,
giving equipment and services (education, training, consulting, etc.) to
local churches, schools may qualify.
- Original Message -
From: "Michael Welch" <[EMAIL PROTECTED]>
To: "RE-wrenches"
Sent: Thursday, Augu
Jeff,
My memory also recalls something about a 6kW value.
I've talked to one of our local utilities about this as well and they base
the accepted imbalance by the size of the transformer serving the building.
I have never read their white paper on the subject though. When I described
a similar s
Greetings wrenches-
Looking for field experience on the GT250 (or GT100). How long has your
install been running? Performance?
Any "gotcha" stories, "heads ups" or advice appreciated. Thanks to all!
For a brighter energy future,
Geoff Greenfield
President
Third Sun Solar & Wind Power Ltd.
340
Well, I must toot my own horn a bit.
Redwood Alliance has been the recipient of a couple used RE equipment donations
in the past. But we are pretty much lined out (except we need a 20 watt system
for a mesh network radio). What we do with other RE equipment donations now is
to turn them into fu