Re: [RE-wrenches] Battery RSD

2025-07-29 Thread david quattro via RE-wrenches
šŸ¤¦šŸ»ā€ā™‚ļø ugh these building departments..! I’m very surprised that they’re requiring the battery conductors to open. I don’t think they understand the gravity of what they’re saying On Tue, Jul 29, 2025 at 10:49 AM MD Electric & Solar < mdelectricso...@gmail.com> wrote: > David, > We already hav

Re: [RE-wrenches] Battery RSD

2025-07-29 Thread david quattro via RE-wrenches
I use the SolArk 12v micro-circuit that triggers RSD. hopefully that’s all they’re looking for, is to kill ESS and solar DC. When using plunger-type, or single gang it’s easy. But when they require a knife blade style switch it’s tricky (with SolArk and Midnite). This is because in order to d

Re: [RE-wrenches] removing old abosolyte cells.

2025-07-17 Thread david quattro via RE-wrenches
If it’s not too steep you can continually leapfrog two or 3 pieces of plywood, and roll your engine dolly on that. Or you can use a few cuts of large diameter pipe as rollers. On Thu, Jul 17, 2025 at 3:33 PM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I was out at the jo

Re: [RE-wrenches] Midnite AIO Battery Low/Lost Behavior

2025-07-16 Thread david quattro via RE-wrenches
One of my customers has a UPS so that Solar Assistant and router don’t rely on the big residential battery bank, in order to keep data flowing. On Wed, Jul 16, 2025 at 5:36 AM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Jason can you remind us what equipment is being used?

Re: [RE-wrenches] Permitting problem

2025-06-25 Thread david quattro via RE-wrenches
For this type of interaction I recommend Engineerinc.com for a Structural stamp. I’ve found them to be very reasonable On Wed, Jun 25, 2025 at 4:03 PM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Friends: > > > > I am having a problem pulling a permit in our coun

Re: [RE-wrenches] charging a 2017 Chevy Volt off-grid

2025-06-23 Thread david quattro via RE-wrenches
I had a similar problem with a Tesla Charger and a golf cart battery charger. Our problems were intermittent. The golf cart charger would balk on GFCI receptacles, but not 'regular' ones. Resolution was: we cleaned up all the ground wires, ground rod itself, clamps, crimps, etc to bright fresh copp

Re: [RE-wrenches] 500V "Crowbar"

2025-06-16 Thread david quattro via RE-wrenches
Travis, sounds like you are not able to re-string the array to conform to 500V max? On Mon, Jun 16, 2025 at 1:42 PM Travis Knipple via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi all, > > This is a repeated (rephrased) version of a previous question, but I've > hit upon a new app

Re: [RE-wrenches] Solar thermal covering

2025-06-15 Thread david quattro via RE-wrenches
There must be a variable mixing valve that is informed and controlled by a thermocouple On Sun, Jun 15, 2025 at 4:46 PM Jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi all > > I’ve inherited an incorrectly sized solar thermal evacuated tube system. > It’s too many tubes for

Re: [RE-wrenches] Sol-Ark Tech Support - Getting Nowhere

2025-06-15 Thread david quattro via RE-wrenches
sounds like you don’t want to take them to small claims court. I found it to be easy and very effective. Did you try switching which inverter is the lead vs follower? On Tue, Jun 10, 2025 at 4:07 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I’m once again

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread david quattro via RE-wrenches
g label. Compared to SolarEdge, Sol-Ark appears fast and > competent. > > As far as labor compensation, who else beside Enphase is paying out? > > Aloha, > Lou Russo > Spree Solar Systems LLC > C-34322 > > > > On Wed, Jun 4, 2025 at 2:09 AM david quattro via RE-

Re: [RE-wrenches] Sol-Ark Warranty Support

2025-06-04 Thread david quattro via RE-wrenches
A few years ago I took SolArk to small claims court. I kept meticulous records, logging months of their disappointing denials and botched tech support. SolArk legal department tried to shift legal jurisdiction from my local country to their Texas jurisdiction. It was an insult to my intelligence. N

Re: [RE-wrenches] Cell damage leading to ground fault?

2025-05-08 Thread david quattro via RE-wrenches
Fronius install manual says the conduit entry ports need to be packed with putty around the wires. They’re the only manufacturer I know of that requires this. Water vapor roses into the circuit boards.I used to get a couple different error codes until we packed the conduits. Good luck, and l

Re: [RE-wrenches] Off-Grid Whole House RO

2025-05-08 Thread david quattro via RE-wrenches
I’ve had good experience with installing a five or 10 second delay on one of the pumps. This way the pumps’ start-current spikes are staggered On Thu, May 8, 2025 at 12:38 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Water pump is not my strong suit. I usuall

Re: [RE-wrenches] String fuse blown

2025-04-11 Thread david quattro via RE-wrenches
One time I had similar, but different problem: 1 Amp ground fault fuse consistently blowing, sometimes after 1 day sometimes after weeks/months. I tried everything - replaced home runs, checked VOC, VMP, swapped DC input into a different inverter, etc. it kept coming back to this one string. I che

Re: [RE-wrenches] Insulation Resistance Testing with Klein ET600

2025-04-06 Thread david quattro via RE-wrenches
Tech support said if it’s landed in conjunction with the Load Out ground it causes an ā€˜echo’ on the grounds. Can result in erroneous Arc fault or other error codes. I think if using a separate wire trough, that trough needs to be physically far from the inverter and close to an electrode. On Su

Re: [RE-wrenches] Insulation Resistance Testing with Klein ET600

2025-04-06 Thread david quattro via RE-wrenches
Hi Jason, SolArk tech support has told us to land the PV equipment ground directly to an electrode. ie do not land the PV ground in the inverter’s built in ground-bar. This detail wasn’t in their manuals years ago. I hope this is helpful šŸ¤™šŸ¼ David On Sun, Apr 6, 2025 at 7:19 AM Jason Szumlansk

Re: [RE-wrenches] 210.8

2025-03-20 Thread david quattro via RE-wrenches
Is there a different engineer you can hire to stamp this job? On Thu, Mar 20, 2025 at 10:11 AM William Miller via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Jay: > > > > 3R is for protection from falling water, like rain or dripping water. > This is not protection against sprayi

[RE-wrenches] SolarEdge refusing their bad inverters

2025-02-17 Thread david quattro via RE-wrenches
Today I learned that Solaredge will not accept responsibility for the E-Waste they generate. They refuse to reimburse installers who are stuck with it. In my experience SolarEdge has a very high failure rate. My local e-waste facility doesn't accept solar inverters. -- David Quattro CA License # 9

Re: [RE-wrenches] RSS: Is it necessary?

2025-02-17 Thread david quattro via RE-wrenches
od > equipment properly and hold manufacturers accountable for shoddy > solutions. If RSD is not that effective we need to discuss undoing the > code requirements. > > > > Sincerely, > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atas

[RE-wrenches] anyone have experience with AMPT DC-DC voltage converters

2025-02-13 Thread david quattro via RE-wrenches
Hi everyone! My financial partners and I are considering replacing all the old modules on a commercial agricultural customer (PGE territory), and this AMPT mfr technology looks promising. Has anyone in this group already tried it? Do they have a high/low failure rate? Do they work as advertised

Re: [RE-wrenches] PV watts question

2025-01-27 Thread david quattro via RE-wrenches
Jay you are right - that doesn’t make sense because with more PV, the system will reach ā€œmax AC outā€œ power sooner every morning and hold it longer into the evening On Mon, Jan 27, 2025 at 12:20 PM George McClellan via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Probably due to cl

[RE-wrenches] big copper wire order

2025-01-23 Thread david quattro via RE-wrenches
Hi All, I need to place an order for about 19,000 ft of 1/0 copper. The conduits are underground and already existing. They were done via directional bore. If I could use Aluminum wire I would. I can't. Which supplier do you recommend for this quantity? Obviously hoping for a volume discount. S

Re: [RE-wrenches] Obscure PG&E NEM 3 question for CA Wrenchers

2025-01-15 Thread david quattro via RE-wrenches
Years ago I had a customer who was dead set against a Smart meter. PGE fought them, but the customer was insistent. There is a way, but PGE charged an additional fee to keep the mechanical disc style meter, because they have to pay an employee meter reader. With NEM3, PGE is almost certain to r

Re: [RE-wrenches] ATS models to bypass GT hybrid inverters for maintenance/faults

2025-01-14 Thread david quattro via RE-wrenches
I’ve been doing this for a few years now, but not on every install. They’re pretty expensive, more labor, one more component to fail, and takes up significant wall space/aesthetic factor. GENERAC transfer switch requires you to rig a separate 12v power supply, (normally this 12vdc comes from th

Re: [RE-wrenches] PG&E NEM3.0

2025-01-13 Thread david quattro via RE-wrenches
Yes count me in On Mon, Jan 13, 2025 at 5:32 PM MDElectricSolar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I say yes please. This is a major change happening and I would like to be > as informed as possible. I understood that the billing change had been > delayed but it sound

Re: [RE-wrenches] SolarEdge

2024-12-13 Thread david quattro via RE-wrenches
If it’s tilt-up arrays, it’s definitely worth it. If it’s flush Mount then.. maybe. I’d tell the owner you simply don’t want to maintain it with Solaredge components. They can either find a different contractor, or let you upgrade the inverters. In my experience Solaredge had a high failure rat

Re: [RE-wrenches] Panel installation in snow country 0.02

2024-12-08 Thread david quattro via RE-wrenches
Here is a very interesting video about vertically mounted bifacial modules - performing surprisingly well. https://www.youtube.com/watch?v=xD1MT-ek05w On Sat, Dec 7, 2024 at 4:36 PM John Blittersdorf via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I'm starting to think that Vert

Re: [RE-wrenches] Sunny Portal

2024-12-03 Thread david quattro via RE-wrenches
SMA monitoring is alive and well. They did migrate to a new platform. It’s called EnnexOS. Depending on the age of your install it might need some attention getting you to the new OS. If it's a commercial install you will have to upgrade to their new Datalogger, as the old ClusterController isn’t

Re: [RE-wrenches] More Issues with Parallel Sol-Ark 15K System

2024-11-10 Thread david quattro via RE-wrenches
SolArk tech support told us that the PV array ground shouldn’t land on the inverter ground bar. But instead should be run to its own local electrode. or if you're grid tied it can land on the ground bar at the Main AC On Sun, Nov 10, 2024 at 6:27 AM Jason Szumlanski via RE-wrenches < re-wrenche

[RE-wrenches] CTs to trigger a high current disconnect

2024-10-25 Thread david quattro via RE-wrenches
Hi Wrenches, Such an honor to address you gurus with this question. I need to monitor current on wires (split phase 240v) and if the current reaches a predetermined limit, let's say 100A, or 200A - I need a programmable meter/device that can trigger a 12v relay when current reaches the threshol

Re: [RE-wrenches] mounting to a foam roof

2024-10-25 Thread david quattro via RE-wrenches
ProSolar posts bolted directly to the wood decking and into rafters. they make several different post-heights. Roofers can easily waterproof cylindrical penetrations. the owners need to decide how many inches of foam thickness On Fri, Oct 25, 2024 at 3:18 PM jay via RE-wrenches < re-wrenches@li

Re: [RE-wrenches] Nice wedge

2024-10-18 Thread david quattro via RE-wrenches
Agreed 100. Pitch hopper is the real deal On Fri, Oct 18, 2024 at 6:13 PM MD Electric & Solar via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Yes, my guys love them! Just makes being on the roof a little easier. > Mike > > On Fri, Oct 18, 2024 at 6:01 PM Nicholas Ponzio via RE-w

Re: [RE-wrenches] sol ark battery

2024-10-09 Thread david quattro via RE-wrenches
I’ve had good experience with Homegrid so far. > > On Oct 9, 2024, at 11:32 AM, jay via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > > > > HI All > > > > > > Wondering what people are using for lithium battery and sol ark? > > > > And no, LA is not a option for this system. > >

Re: [RE-wrenches] UL3741

2024-10-08 Thread david quattro via RE-wrenches
This is an excellent explanation of many aspects of 3741. https://youtu.be/mgD0O9WfKVU?si=-SRdLuTd4XGDToKp At the NABCEP conference in Raleigh earlier this year, there were popular presentations about 3741. I think it can be a great solution for some small commercial, but not for residen

Re: [RE-wrenches] favortie micro inverters?

2024-09-23 Thread david quattro via RE-wrenches
I used Chilicon on a couple installs, and Enphase is far better. On Mon, Sep 23, 2024 at 9:05 PM greg egan via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Good intel. I believe their micros are rated to -40C/F. If they quit > working at that temp it would be okay as long as th

Re: [RE-wrenches] ATS Brand Recommendations

2024-09-20 Thread david quattro via RE-wrenches
Nice. I’ve considered using a little jump battery once or twice but still haven’t had to. I put on my calendar ~3 years replace all gen-start FLA batteries because the consequences of them going dead are pretty bad. Curious if you guys think 3 years is a good rule of thumb. __

Re: [RE-wrenches] ATS Brand Recommendations

2024-09-20 Thread david quattro via RE-wrenches
I have had good experience with Kohler transfer switches but only the simpler RDT models should be used in conjunction with a complex custom system. (Kohler’s cheaper RXT models require a keep-alive signal from a Kohler generator) ___ List sponsored

Re: [RE-wrenches] ATS Brand Recommendations

2024-09-20 Thread david quattro via RE-wrenches
I have a system with Generac ATS where Grid is Primary source, SolArk Critical Load is secondary source. And whole home is the Load out of the ATS. Generator feeds in to the SolArk Gen terminals. KOHLER generator (2-wire auto start) engages only when the SolArk tells it to, programmed by me a

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
Sorry I just noticed that you’re dealing with 15Ks. My scenario was with a 12K ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
last year SolArk tech support told me only the Gen ports have the freq/volt modulation, and only when you program the master ā€œAC Couple on GENā€ ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE

Re: [RE-wrenches] discover lithium warranty issues.

2024-08-19 Thread david quattro via RE-wrenches
If a manufacturer decides to pettifog over a property being sold in order to escape warranty obligation.. yikes! no thanks On Mon, Aug 19, 2024 at 3:04 PM Maverick Brown via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Luke > > I appreciate the follow up. > > And as a/an FLA/AGM

Re: [RE-wrenches] Portable systems

2024-08-16 Thread david quattro via RE-wrenches
I have two Jackery units and both are great. small 500W and the other is either 2 or 3kW On Fri, Aug 16, 2024 at 2:55 PM Hilton Dier, III via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I've got someone asking me about a portable system. It really doesn't have > to be that portable.

Re: [RE-wrenches] Neutral run to critical loads sub-panel

2024-07-30 Thread david quattro via RE-wrenches
Definitely best practice to do so, in fact probably not safe as it’s wired now. I know some inverters won’t work at all with ā€œneutral loopsā€ and are sophisticated enough to feel it, and stop inversion until the electrician fixes it On Tue, Jul 30, 2024 at 5:48 AM Jason Szumlanski via RE-wrench

Re: [RE-wrenches] Sol-Ark with 800A Service

2024-07-17 Thread david quattro via RE-wrenches
Hi Chris, I’ve asked them if they are compatible with rope CTs and they aren’t…. Please share the solution you arrive at, as I know I’ll need to repeat it soon. David ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wre

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread david quattro via RE-wrenches
in their installation manuals, SolArk indicates black and red colors for PV conductors. ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Sol-Ark Support

2024-06-05 Thread david quattro via RE-wrenches
Today they tried launching their monitoring migration from Inteless/PVPro to Mysolark/solarkcloud.com I had several sites throwing multiple bogus error codes and concerned homeowners calling my staff all morning. SolArk tech support probably drowning in that Error codes:: F49 Backup_Battery_Fault

[RE-wrenches] REC modules - review?

2024-05-17 Thread david quattro via RE-wrenches
Hi everyone, Does anyone have positive or negative experience with REC modules? Specifically failure rate, and how the company acts when an RMA is necessary. Thank you David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com __

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-05-03 Thread david quattro via RE-wrenches
I think SolArk makes an 8K 120V-only version David On Fri, May 3, 2024 at 3:13 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > For this application I was originally thinking about a 48V inverter with > 120V output, but there are not many options in the size ra

Re: [RE-wrenches] Anybody else caught up with the Lumos urgent recall?

2024-04-22 Thread david quattro via RE-wrenches
wow. Sounds like a class action lawsuit if they’re not careful. I’ve never heard of any module manufacturer pay for lost production, but they need to cover parts and labor or they will be sued, and they will lose. ___ List sponsored by Redwood Allianc

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread david quattro via RE-wrenches
OK thanks for the correction. It's confusing to me because the external chassis is identical ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver

Re: [RE-wrenches] midnite new inverter

2024-04-10 Thread david quattro via RE-wrenches
I have not installed an Fortress yet, but I know they are made by Deye (same Chinese original manufacturer as SolArk inverters) Here is a link for an excellent instructional by Steve Higgins @ Rolls - https://www.youtube.com/watch?v=RJqBULN9MgI&pp=ygUWcm9sbHMgc3VycmV0dGUgaGlnZ2lucw%3D%3D This assum

Re: [RE-wrenches] Plaques

2024-03-30 Thread david quattro via RE-wrenches
Generic stickers are easily gotten but site-specific placards are often required. I recommend Tony ::: Tony Nguyen We send him a PDF doct and the size/font requirements. within a couple days I receive a perfect red placard with white lettering, 3M sticky on the back, at very reasonable pricing. T

Re: [RE-wrenches] Enohase tech support

2024-03-15 Thread david quattro via RE-wrenches
Jason, Very helpful. Thank you I wonder why, after years of calling tech support, nobody at Enphase told me the S is a replacement for the R. it took a compatriot installer/integrator to care enough. On Fri, Mar 15, 2024 at 2:51 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: >

Re: [RE-wrenches] Enohase tech support

2024-03-15 Thread david quattro via RE-wrenches
wow, your experience is worse than anything I've ever heard of from Enphase tech support. My experience with them is this: they know their old Envoys are garbage (the M-Series are failing left and right now). The executives made the decision that they will no longer manufacture new M-Envoys. I don'

Re: [RE-wrenches] 30% ITC

2024-02-28 Thread david quattro via RE-wrenches
I thought the primary goal of the federal ITC was to address climate change. Thus as a citizen of Earth, increased PV adoption is success regardless of whatever financial implications arise from a taxpayer perspective. ___ List sponsored by Redwo

Re: [RE-wrenches] Fwd: Re: $300 + transmission fee!

2024-02-26 Thread david quattro via RE-wrenches
Hi William, I’ve never done this but talked to the electrical/electronic engineer who did:: he took all the CT current, and voltage inputs and ran them into a small cheap Linux PC, which was easy to find support and used a common programming language. These guys only used it for a custom moni

Re: [RE-wrenches] Fwd: Re: $300 + transmission fee!

2024-02-26 Thread david quattro via RE-wrenches
Jay, there are three major utilities in CA. I don’t know much about LADPW nor SDGE. PGE executes demand charges depending on the ā€˜rate schedule’ applied to a specific meter. Customers can request to change their rate schedule, sometimes with significant financial savings just doing that. M

[RE-wrenches] LG Battery charger instruction

2024-02-20 Thread david quattro via RE-wrenches
Hi Tom, a few years ago I decided to buy my own LG battery charger because we needed the damn thing so often. Now I only use it once or twice per year, because I stopped installing LG batteries. Here is the instruction I have which works on my charger (same charger as the LG-sanctioned :: the man

Re: [RE-wrenches] No payment for Sunpower warranty service vendor credits?

2024-02-13 Thread david quattro via RE-wrenches
Yes SolArk can be programmed to sell the battery energy in specific time windows David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com On Tue, Feb 13, 2024 at 3:37 PM Darryl Thayer via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Advice, please; I w

Re: [RE-wrenches] Automatic load control

2023-12-15 Thread david quattro via RE-wrenches
SPAN Panel, or you can try Generac 7006 automatic load shed device (100A) https://apelectric.com/generac-7006-smart-management-module/ Or G7000 (50Amp) I’ve heard they work with other inverters, not just GENERAC only, but of course you’d have no warranty when mixing brands. David On Thu, Dec 14

Re: [RE-wrenches] Radian Question

2023-10-30 Thread david quattro via RE-wrenches
I’m not familiar with Outback defaults but most inverters I’ve dealt with have a grid tolerance of 10% +/- so 216 to 264VAC. On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi Jay, > > The inverter won't even connect to the grid. I

Re: [RE-wrenches] Cleaning PV mods

2023-10-23 Thread david quattro via RE-wrenches
The encapsulant between the glass and the aluminum might be degraded by a surfactant. It’s probably a low risk if you use a gentle soap, but I heard that somewhere about 15 years ago so I thought I’d mention it. I also heard that pressure washers are too strong and can ruin the encapsulant seal

Re: [RE-wrenches] Line Side Tap

2023-10-13 Thread david quattro via RE-wrenches
Dana in your first example it looks like 120A of solar is pushing onto a 100A utility meter, over #3 copper which cannot handle 120A. But I might be missing something. On Fri, Oct 13, 2023 at 6:29 AM Dana Orzel via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Repost of 2 types of

Re: [RE-wrenches] Line Side Tap

2023-10-12 Thread david quattro via RE-wrenches
Drake I think you’re right and they’re wrong, as long as the 200A bus is protected by a 200A breaker, and as long as the Utility meter and utility conductors remain 400 David On Thu, Oct 12, 2023 at 5:06 PM Drake Chamberlin via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > We have

Re: [RE-wrenches] Fronius USA available 2023 & 2024 ?

2023-08-26 Thread david quattro via RE-wrenches
If you’re dealing with PG&E Utility, Fronius decided a few years ago not to play along anymore. PGE constantly changes the requirements for the inverter manufacturers, and what they call Smart Inverters. from what I understand this is mostly for solar curtailment when the grid is saturated. I t

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread david quattro via RE-wrenches
Type 1: You’ll be limited to 100A solar because the Utility conductors you’re attaching to are 100A. The Utility tap needs to immediately go to a fused disconnect switch, generally within 6ft (sometimes 10ft) and within line of sight of the meter. Fuses need AIC rating equivalent to that of the S

Re: [RE-wrenches] SolarEdge Car Charger

2023-07-25 Thread david quattro via RE-wrenches
I haven’t installed a Solaredge in years so my info might not be up to date, but I remember that the EV Charger units couldn’t be commissioned without an active internet connection. The early models had high failure rate, but that was within the first year or two that they offered the EV Charger/i

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread david quattro via RE-wrenches
The cells are cracking. The metal traces are victim (not the cause) along the crack lines-- David Quattro CA License # 954020. C-10, C-46 ph (415) 312-2661 www.quattrosolar.com ___ List sponsored by Redwood Alliance Pay optional member dues here: http:/

Re: [RE-wrenches] Lithium battery recommendation

2023-07-13 Thread david quattro via RE-wrenches
SimpliPhi has given me zero problems over about a dozen systems. so far I have only used the 3.8kWh units that are not capable of closed loop communication. On Thu, Jul 13, 2023 at 9:34 PM Carl Hansen via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Peter, > >I've also insta

Re: [RE-wrenches] LG Chem RESU10H Battery Question

2023-06-30 Thread david quattro via RE-wrenches
Hi David and David, it’s me David Since no lights come on when you turn the breakers on, it sounds like the battery is deeply discharged. I bought a specialized charger for the RESU10H. If you want to borrow it let me know. David Quattro On Fri, Jun 30, 2023 at 10:40 AM Dave Angelini Offgri

Re: [RE-wrenches] High current dc combiner vibration

2023-06-30 Thread david quattro via RE-wrenches
Ferrite cores can be used for the battery cables to pass through to reduce common mode current On Fri, Jun 30, 2023 at 3:59 AM Kirk Herander via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I have -15- sets of 4/0 cable (1 per 32 kwh stack) into the combiner. They > are paired and wi

Re: [RE-wrenches] Remote load shedding

2023-06-27 Thread david quattro via RE-wrenches
GENERAC also makes a 100 amp version of the SMM On Tue, Jun 27, 2023 at 3:12 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I'm interested in this also. This is becoming increasingly necessary as we > install "whole home" backup systems, but we need to dump a

Re: [RE-wrenches] Fronius primo fan

2023-06-15 Thread david quattro via RE-wrenches
Hi Jay, in my experience most fans are readily available, you just have to pull the old fan and get a part number from its nameplate. Or you can probably order one from Fronius tech support. Worst case I experienced was on an old SHARP inverter (3 MPPT's), it was supposed to be 3-wire fan, but all