Re: [RE-wrenches] Late 2010 Report: Magnum Advanced Remote & Magnum Switchgear

2010-12-23 Thread Brian Faley
Thanks Mick for the post we always welcome feedback from installers
after all you guys are the experts! A couple of notes to clarify Mick's
observations.

Mick is correct, the version 2.1 of the ME-ARC release Feb 2010 did have
a software bug where the decimal point was in the wrong place in the
Amps IN/OUT meter. The calculation for the SOC meter was still correct
so the actual SOC displayed was correct but the individual meter was
wrong by a factor of 10. The bug was reported in May 2010 and the fix
(along with some new features) was released Nov 2010. We apologize for
the inconvenience this bug caused but we didn't recall the product as
the SOC was still correct, which is the most critical meter to determine
battery SOC. 

Again thanks for your insight on the MMP and MP panels. We use Torx
fasters not as a deterrent but because the sheet metal is "funnel
punched", which means when we receive it there are no threads for the
screws. We use a special thread forming screw (not to be confused with
self tapping screws, thread forming screws leave no metal shavings when
forming the threads) to drive into the sheet metal which takes some
force to achieve the threads. We use Torx instead of Phillips heads
because Phillips heads screws strip out to easily during the process of
using the thread forming screws. We have used Torx thread forming
fasteners in our products from the very inception of Magnum and you may
notice they hold the top covers and all the boards together in the
inverters.

The original MMP units did not have a charge controller bracket. It was
added later as were the PEM nuts for the mounting to the MMP, so there
are no holes to drill on the current MMP. The charger controller bracket
fits the right or left hand side and fits: MidNite, Outback and
Morningstar controllers. The controller is mounted with the nipple at
the bottom and the bracket holds the top of the controller from
"pivoting". For the Outback controllers there is also a hole in the MMP
if you want to take one of the controller cover screws out you can
reinsert the screw through the MMP into the controller.

The last item I will mention is the lack of a bracket to mount the
standard remote to the MP panels. The MP panels are designed for
multiple parallel inverter installations which a ME-RTR (we call it a
router, like a Hub and Mate in one unit) is required so you can parallel
two or more inverters. We do provide a router bracket since most likely
you would use an MMP for one inverter and the MP for multiple inverters.

Hope this helps, and again thanks Mick your insight.


Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
bfa...@magnumenergy.com



> Message: 8
> Date: Wed, 22 Dec 2010 18:02:44 -0700
> From: Mick Abraham 
> To: RE-wrenches 
> Subject: [RE-wrenches] Late 2010 Report: Magnum Advanced Remote &
>   Magnum  switchgear
> Message-ID:
>   
> Content-Type: text/plain; charset="iso-8859-1"
> 
> Greetings, Mechanix~
> 
> The ARC-50 product from Magnum Energy--the Advanced Remote--has some
> features not available on the regular RC-50--such as an internal clock
to
> manage things like generator quiet time. The ARC-50 is much less
navigable
> compared to the RC-50 but that's understandable.
> 
> Here's a warning about a "zero day defect" in the firmware on the
ARC-50.
> Version 2.1 is the first one that has been shipping and this version
will
> not play nice with the BMK Battery Monitoring Kit from the same
company.
> The
> glitch is subtle and not easily recognized but the "amp hours from
full"
> counter in the BMK counts incorrectly--by a factor of ten.
> 
> Version 2.2 is now available but I believe Magnum has not issued a
recall
> of
> the early version so some of the old firmware may be sitting on the
> shelves.
> I was not pleased to learn that Magnum had known about this
problem--and
> even had named it internally--but was continuing to ship product with
the
> buggy code. The company will upgrade the firmware for existing units
but
> they do not offer any hassle compensation for the installers.
> 
> 
> 
> I have recently worked with the Magnum Mini Panel (R) and also with an
> MPSL-version (bigger) control box. Here's a report that some of the
> Mechanix
> may find useful. Disclosure: I gain nothing from the switchgear
choices
> which are made by my fellow installers, so this is unbiased feedback.
> 
> Both of these Magnum control boxes use Torx fasteners extensively so
just
> getting the front cover off requires a tool quest beforehand. At least
> they're not tamperproof Torx but one still must wonder why obstacles
must
> be
> erected. It's not like there are radioactive components inside.
> 
> Both of the above ment

Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter

2011-04-13 Thread Brian Faley
Esteemed Wrenches,

There are other battery based inverters with Frequency Shift for use in
AC coupled systems. Magnum MS4024PAE and MS4448PAE models shift the
output frequency + >0.5Hz based upon battery voltage. On 24V models the
set point is 0.2V above absorb voltage, and on 48V models it is 0.4V
above absorb. It will protect the battery against overcharge by dropping
the AC coupled Grid tied inverter offline. It can be used as a method of
regulating AC coupled grid tied systems, but works best when there is a
DC side diversion load controller.

Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
bfa...@magnumenergy.com
 
> --
> 
> Message: 3
> Date: Tue, 12 Apr 2011 21:37:06 -0700
> From: "Mark Frye" 
> To: ,   "'RE-wrenches'"
>   
> Subject: Re: [RE-wrenches] AC Coupling Fronius IG Plus 10.0 inverter
> Message-ID: <0FAC7002A96948B598E5EF79FF3D77E6@marksdell>
> Content-Type: text/plain; charset="us-ascii"
> 
> Gary,
> 
> I have been looking at some AC coupled stuff lately. The "FSC" is
> propriatary to SMA, Sunny Island to Sunny Boy.  Pretty much anything
else
> you need something to sense the voltage of the battery bank so you can
> open
> a contactor on the AC line to the Fronius when the battery voltage
gets
> too
> high. Once the voltage drops the contactor can close and bring the
Fronius
> back on line and then the 5-minute start up delay before it is feeding
the
> line again.
> 
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City,  CA 95959
> (530) 401-8024
>  <http://www.berkeleysolar.com/> www.berkeleysolar.com

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling

2011-09-02 Thread Brian Faley
Hi Larry, 

Magnum MS PAE inverters do indeed shift the inverter output frequency
when the battery is full in order to disconnect grid-tied inverters used
in AC coupled systems. It was designed to work in conjunction with a DC
diversion load - which is recommended if the system is larger than a
couple panels.


Regards,


Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
bfa...@magnumenergy.com
 
> 
> Larry Brown wrote:
> > Wrenches,
> >
> > After Hurricane Irene left a lot of people without power here in the
> > Northeast, customers who have grid-tied systems are asking about
some
> > battery backup to power some essential loads.
> >
> > We have used Sunny Islands but they require either 2 Sunny Islands
or
> > a step up transformer to get 240 volts for the well pump.  Schneider
> > Electric  (Xantrex XW) inverters look like they would work  for this
> > application and do 120/240 volt output as well and we have used
these
> > in off grid applications but not as AC coupled.  I have considered
> > Magnum because they also do 120/240 volts but they need battery
> > diversion to ensure the batteries are not over charged.
> >
> > None of these systems are going to be rewired as a DC system so I am
> > looking for any feed back on what others are using to AC couple to
> > existing grid-tied systems to provide some battery backup.
> >
> > Thanks
> > Larry
> >
> > Larry Brown
> > Sun Mountain___
> >
> >
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling

2011-09-02 Thread Brian Faley
Hi Allen,

 

I'll try to describe the typical AC coupled system as well as I can.

 

In such a system, a NON-grid tied battery based inverter (i.e. Magnum MS
PAE) is connected as a backup inverter, only supplying AC power to
consumer's loads when the grid is down. The micro inverter(s), or string
inverters are connected on the load side of the inverters transfer
switch, in parallel with the inverter output so they see AC grid power
(when available) or inverter power when the grid goes down. The micro
inverters / string inverters in such a system are called AC coupled
inverters because the point of coupling is the AC system rather than the
DC system. This allows the battery based inverter to provide the grid
reference to the AC coupled grid-tied inverters when the utility power
is not present - Backup mode. In that mode the inverter will form the
reference for the grid tied inverters and any surplus power supplied by
the grid-tied inverters that is not being consumed by AC loads will
charge the battery of the inverter.  In this inverter mode, once the
battery is full, the inverter senses it and shifts the inverter
frequency by .5hz to force the grid tied inverters off, keeping them
from exporting power, thereby stopping the battery from overcharging. 

 

On a large system, a DC diversion load is usually added in parallel with
the battery to reduce the on/off cycling of the grid tied inverters,
which once the frequency shift happens, will try to reconnect every five
minutes without it. 

Using the frequency shift method only is rather crude, because it
essentially is a bang/bang controller - off or on. Its not a matter of
our lack of confidence in the approach, the question is do you want the
battery voltage swinging around by several volts. In a DC diversion mode
system, the surplus energy from the grid tied inverters can be put to
work as a useful dump load rather than just off lining several kw of PV.


 

We had a white paper describing the AC couple mode. I'll see what we can
do to make it more widely available, since the interest in such systems
seems to be increasing.

 

 

 

 

 

Brian Faley

Chief Engineer

Magnum Energy

2111 W Casino Rd

Everett, WA 98204

425-353-8833

bfa...@magnumenergy.com

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Friday, September 02, 2011 4:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling

 

Brian,
Could you speak a bit more to this, please? My understanding is that the
need with a string (or, I suppose, micro-) inverter and a battery-based
inverter is for a way to disconnect full batteries from being
overcharged when the grid is down and sell is disabled. The SMA approach
is to shift frequency to reduce string inverter output. I thought that
the battery-based (Outback, Magnum) approach is to use a contactor to
open string inverter AC based on voltage (crude, but effective). 

So what I understand is that the PAE inverters shift frequency: do you
mean it simulates the shift that a Sunny Island would do? And if so, why
is a diversion load recommended, and how is it configured into the
system? And where can we read more about how this is designed to work?
Thank you,
Allan
 

Allan Sindelar
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com> 
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  


On 9/2/2011 4:39 PM, Brian Faley wrote: 

Hi Larry, 
Magnum MS PAE inverters do indeed shift the inverter output frequency
when the battery is full in order to disconnect grid-tied inverters used
in AC coupled systems. It was designed to work in conjunction with a DC
diversion load - which is recommended if the system is larger than a
couple panels.
 
Regards,
 
Brian Faley
Chief Engineer
Magnum Energy
2111 W Casino Rd
Everett, WA 98204
425-353-8833
bfa...@magnumenergy.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC Coupling

2011-09-06 Thread Brian Faley
Kent,

 

Yes, that is the drawing of a typical installation.

 

Regards, 

Brian

 

Brian Faley

Chief Engineer

Magnum Energy

2111 W Casino Rd

Everett, WA 98204

425-353-8833

bfa...@magnumenergy.com

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Saturday, September 03, 2011 1:47 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling

 

Brian,



Is this the drawing?

Magnum ac coupled diagram
<http://www.google.com/url?sa=t&source=web&cd=1&sqi=2&ved=0CBYQFjAA&url=
http%3A%2F%2Fwww.magnumenergy.com%2FLiterature%2FApplication%2520Info%2F
Magnum%2520AC%2520Coupled%2520Line%2520Diagram%2520%281-May-2010%29.pdf&
rct=j&q=%22ac%20coupled%22%20site%3Awww.magnumenergy.com&ei=EZBiTte-H4jn
iAKNraDGCg&usg=AFQjCNG7FuyVaDx7YSWcJfqkh4TUkps4qA&cad=rja>  from Google
cache.



Kent Osterberg

Blue Mountain Solar








 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Component Choices for MY RV - Apollo Solar?

2010-07-01 Thread Brian Faley


Hi Jeff,

Just a couple comments to answer your question about Magnum inverters.
See below.
> 
> Message: 6
> Date: Thu, 1 Jul 2010 06:09:35 -0700
> From: Jeff Clearwater 
> To: RE-wrenches 
> Subject: [RE-wrenches] Component Choices for MY RV - Apollo Solar?
> Message-ID: 
> Content-Type: text/plain; charset="iso-8859-1" ; format="flowed"
> 
> Dear Colleagues,
> 
> Well this one's for me!  Nice to do solar for
> oneself after installing for others my whole life!
> 
> I'm putting together an small RV system in my
> Sprinter Van that will also act as a small mobile
> power platform.  SUGGESTIONS?
> 
> I'm considering the following:   What would be better???
> 
> Batteries:  6 or 8 Optima Blue Tops (12 Volt
> System - possibly 24V) (space is limited - it's a
> 144" Sprinter Van)  - Other sealed alternatives
> you think are better?
> 
> Modules:  2 Sanyo HIP-195BA19s (have already)  &
> 1 undetermined 90-120 watt module (all that will
> fit!)  (Anyone have an extra BP 790 or an
> AE-90HE, AE-120HE??? or other 24" x 48" ish
> module?)
> 
> Charge Control:  OB FlexMax 60  or should I wait
> for the Midnight Classic?  (A Sunsaver MPPT will
> be used for the 100 watt module).  (I'll also be
> dumping extra power to hot water).  Or Apollo if
> I use the Apollo inverter below.
> 
> Inverter:  I'd like to eventually have 120/240 so
> I could build from the RV.  So question is:
> 
> A) One Outback 2012 now and then add another for 240 VAC later OR
> B) Apollo TSE2212  OR
> C) Magnum MS 4024 (in which case I'd have to go
> with a 24V pack and a 24>12 DC>DC for 12V loads)

The Magnum MS4024 is a 120V inverter for AE and mobile applications. The
MS4024AE is a 120/240 split phase inverter for AE applications. 
> 
> Monitoring:  OB Mate (Flexnet?) or (Apollo ASNET if I go Apollo).
> 
> QUESTIONS?
> 
> 1)   Opinions of the Blue Top vs ???
> 
> 2)  Best RV inverter - Outback?  Apollo?  Magnum?
> Experience?  Vibration?  Only the Outback offers
> neutral switching in the transfer switch. (Does
> the Magnum?).

Magnum MS4024 (120V single phase output) has neutral/gnd switching in
the transfer switch of the inverter. It is ETL listed to UL458 (mobile
inverters) AND UL1741.
The MS4024AE is a 120/240 split phase inverter intended for AE use
(non-ground switched) It is ETL listed to UL1741.

  Weight is an issue as well as
> space.

MS4024 4kW inverter 55lbs
> 
> 3)  Charge Control - Is the Classic Shipping?
> 
> Thanks for your time!
> 
> Best,
> 
> Jeff C.
> 
> --
> ~~~
> Jeff Clearwater
> Village Power Design
> 
> Solar Design Consultation for the Commercial Sector
> http://www.villagepower.com
> goso...@villagepower.com
> 
> NABCEP Certified Solar PV Installer ?
> http://www.nabcep.org/
> 
> Voice: 831-427-2799
> Fax: 413-825-0703
> 245 Dufour St
> Santa Cruz, CA 95060
> ~

Regards,
Brian Faley
Chief Engineer
Magnum Energy, Inc
2211 West Casino Rd, Everett, WA 98204
425-353-8833 voice
bfa...@magnumenergy.com
www.magnumenergy.com


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Wood boiler ignition issue

2012-03-27 Thread Brian Faley
Hi Kris,

 

A solution to try would be to add a motor run capacitor across the line
at the boiler.  10uF-20uf range may improve the crossover distortion
enough to allow the boiler ignitor to operate properly. Start with 10uF.


 

Regards,

Brian

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Kristopher Schmid
Sent: Monday, March 26, 2012 11:51 AM
To: RE-wrenches
Subject: [RE-wrenches] Wood boiler ignition issue

 

Esteemed wrenches,

I am assisting in troubleshooting a stand alone system with three
stacked Magnum 4448 PAE inverters.  The electric ignition of LP for the
wood boiler will not fire from inverter power.  As soon as we fire up
the generator, the boiler ignites.  Has anyone seen this before?  Is
there a solution?  The boiler is a Central Boiler E-Classic 2400.

Thanks in advance!

--
Shine On!

Kris Schmid
Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
www.legacysolar.com
NABCEP Certified PV Installer
BSEE 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Wood boiler ignition issue

2012-03-27 Thread Brian Faley
Larry,

 

Very likely it would work for the washer as well. Grainger (or another
industrial supply company) has 10uF 370Vac oval can motor run caps for
under 9 bucks. 

 

Regards,

Brian 

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher,Starlight Solar Power Systems
Sent: Tuesday, March 27, 2012 3:21 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Wood boiler ignition issue

 

Brian,

 

Would this also work for the Splendide washers? If not, have you come up
with any solution yet?


Larry Crutcher

Starlight Solar Power Systems

(928) 342-9103

 

 

 

On Mar 27, 2012, at 2:04 PM, Brian Faley wrote:





Hi Kris,

 

A solution to try would be to add a motor run capacitor across the line
at the boiler.  10uF-20uf range may improve the crossover distortion
enough to allow the boiler ignitor to operate properly. Start with 10uF.

 

Regards,

Brian

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum Energy Remote Control

2012-06-28 Thread Brian Faley
Hi Jeff, Wrenches,

 

Magnum specifically designed the ARC (Advanced Remote Control) for
off-grid applications so that all of the possible custom settings are
available. We strongly recommend it for several reasons:

 

1)  A customer without a remote is left with no information on
inverter operation or troubleshooting.

2)  Even if they have a simple question it results in a phone call
either to the factory or dealer, leaving the customer feeling helpless.

3)  It reduces service calls and provides piece of mind to the
customer who now has the ability to see what is going on with their
system.

4)  It provides status information about their battery, AC/Gen
input, inverter operating point and charging current.

 

One of the main reasons for dealers not wanting to leave a remote is
that customers have a tendency to "push buttons" and mess things up. The
Magnum ARC has password protection for the SETUP button,  plus it is
much easier to navigate than other remotes so customers have a much
easier time understanding the remote.

 

The Magnum remote controls store the user settings internally in
non-volatile memory. An inverter may be 'programmed' by plugging a
remote into it - thus transferring the settings to the inverter. The
remote may then be unplugged from the inverter and the custom settings
remain in the inverter until DC power to the inverter is reset. 

 

Here are some of the features of the ARC

 

1)  Has all the settings required for offgrid and backup power

2)  All Auto Gen Start and Battery Monitor settings and displays are
included

3)  Password protected SETUP button for those desiring to lockout
end users

4)  FAVS button allows limited access to settings end users may need
on occasion without a password

5)  CTRL button allows manual control of  a generator start/stop
(AGS required

 

 

Regards,

Brian

 

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff
Yago
Sent: Thursday, June 28, 2012 7:09 AM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] Magnum Energy Remote Control

 

We recently started stocking the Magnum Energy inverters and when we had
a few installations requiring some adjustments to the default settings
we were advised to order the Magnum Energy Remote Control.  However, we
then found out that this is a stripped down control and we needed to
order the "Advanced" version of this control. 

 

Our plan was to keep this in the assembly area and use anytime we have a
Magnum inverter that needs modification of the setpoints.  However,
after ordering all these different models and controls it appears some
or all of these setpoints in the inverter go back to default if we
un-plug the remote control.  Is this correct??

 

We have many projects that either the client does not want the remote
control, will not pay the extra cost for the remote control, or we do
not want them attempting to change these settings.  Is there a way to
use the remote to make these changes and then ship out the inverter with
the modifications without the needing to include the remote control. 

 

Thanks,

 

Jeff Yago

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Magnum Energy Remote Control

2012-06-28 Thread Brian Faley
Todd,

 

The ARC is the remote control we recommend for use in off-grid systems. 

It also displays information from two additional accessory products: the BMK 
which is our battery monitor which reports state of charge, real time amps, amp 
hours in/out, and minimum/maximum DC volts; and the AGS which is our automatic 
generator starting product.

 

http://magnumenergy.com/Products/productsBatteryMonitor-Combiner.htm 
<http://magnumenergy.com/Products/productsBatteryMonitor-Combiner.htm> 

 

http://magnumenergy.com/Products/productsAGS.htm 
<http://magnumenergy.com/Products/productsAGS.htm> 

 

regards,

Brian

 

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of 
toddc...@finestplanet.com
Sent: Thursday, June 28, 2012 10:59 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Magnum Energy Remote Control

 

i have only done a couple of magnum off-grid systems with the standard 
programming interface, so it is news to me that there is another interface 
available. i need some clarification.

 

this:

 

2) All Auto Gen Start and Battery Monitor settings and displays are included

 

indicates there is a built in amp hour meter then similar to the trimetric?

 

thanks,

 

todd

 

 

 

On Thursday, June 28, 2012 10:29am, "Brian Faley"  
said:

Hi Jeff, Wrenches,

 

 

Magnum specifically designed the ARC (Advanced Remote Control) for off-grid 
applications so that all of the possible custom settings are available. We 
strongly recommend it for several reasons:

 

 

1) A customer without a remote is left with no information on inverter 
operation or troubleshooting.

2) Even if they have a simple question it results in a phone call either to the 
factory or dealer, leaving the customer feeling helpless.

3) It reduces service calls and provides piece of mind to the customer who now 
has the ability to see what is going on with their system.

4) It provides status information about their battery, AC/Gen input, inverter 
operating point and charging current.

 

 

One of the main reasons for dealers not wanting to leave a remote is that 
customers have a tendency to “push buttons” and mess things up. The Magnum ARC 
has password protection for the SETUP button,  plus it is much easier to 
navigate than other remotes so customers have a much easier time understanding 
the remote.

 

 

The Magnum remote controls store the user settings internally in non-volatile 
memory. An inverter may be ‘programmed’ by plugging a remote into it - thus 
transferring the settings to the inverter. The remote may then be unplugged 
from the inverter and the custom settings remain in the inverter until DC power 
to the inverter is reset. 

 

 

Here are some of the features of the ARC

 

 

1) Has all the settings required for offgrid and backup power

2) All Auto Gen Start and Battery Monitor settings and displays are included

3) Password protected SETUP button for those desiring to lockout end users

4) FAVS button allows limited access to settings end users may need on occasion 
without a password

5) CTRL button allows manual control of  a generator start/stop (AGS required 

 

 

 

 

Regards,

Brian

 

 

 

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com <http://www.magnumenergy.com> 

 

 

 

 

 

 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Thursday, June 28, 2012 7:09 AM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] Magnum Energy Remote Control

 

 

 

We recently started stocking the Magnum Energy inverters and when we had a few 
installations requiring some adjustments to the default settings we were 
advised to order the Magnum Energy Remote Control.  However, we then found out 
that this is a stripped down control and we needed to order the “Advanced” 
version of this control. 

 

 

Our plan was to keep this in the assembly area and use anytime we have a Magnum 
inverter that needs modification of the setpoints.  However, after ordering all 
these different models and controls it appears some or all of these setpoints 
in the inverter go back to default if we un-plug the remote control.  Is this 
correct?? 

 

 

We have many projects that either the client does not want the remote control, 
will not pay the extra cost for the remote control, or we do not want them 
attempting to change these settings.  Is there a way to use the remote to make 
these changes and then ship out the inverter with the modifications without the 
needing to include the remote control. 

 

 

Thanks,

 

 

Jeff Yago

 

 

 

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Brian Faley
Hi Allan,

 

In answer to your question: Yes, we're developing an AC side 4kW
diversion mode controller which allows temperature compensated three
stage charging for AC coupled inverter applications.  It is currently in
beta site testing.  

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Thursday, March 07, 2013 2:41 PM
To: RE-wrenches
Cc: Support
Subject: Re: [RE-wrenches] AC Coupled Magnum Issue

 





McAfee SiteAdvisor Warning

 

This e-mail message contains potentially unsafe links to these sites:

 
<http://www.siteadvisor.com/sites/athens-electric.com/?pip=false&premium
=true&client_uid=446795512&client_ver=3.6.0.187&client_type=IEPlugin&sui
te=true&aff_id=0&locale=en_us&ui=1&os_ver=6.1.1.0> 

http://athens-electric.com/

 

 

OK, a bit more:
The line diagram I was referencing was dated 5/1/2010. A later diagram
from a Powerpoint given at last year's NABCEP CE conference shows a
"MagNet" AC diversion controller. It allows AC diversion loads and
three-stage charging. No mention of temp comp.

Magnum needs to weigh in on this.
Allan

Allan Sindelar
al...@positiveenergysolar.com <mailto:al...@positiveenergysolar.com> 
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>  

 

 

On 3/7/2013 3:00 PM, Drake wrote:

Hello Wrenches,

I had an unexpected glitch in AC coupling a Magnum 4024 PAE
inverter.  The system utilizes AGM batteries, which (according to
Concorde tech support) have a very strict upper voltage limit.

The relay used to stop the current input from the direct grid
tie inverter, when battery voltage is high, is controlled by a
Morningstar Relay Driver.  The relay driver is set to shut off the
charge at 28.8 volts.

The charger on the Magnum is set to charge the batteries to
28.6 volts.  

The plan was to be able to charge batteries from the Magnum
without tripping the AC connection between the grid tie inverter to the
grid.  The Magnum should charge to 28.6 volts, 0.2 volts below the relay
driver's programmed trigger point. 

There is one catch to using this approach. The Magnum inverter
has a remote temperature sensor in the battery bank. The relay driver is
not temperature corrected. Therefore, when the batteries are cold, the
charging voltage goes up in the Magnum.  This higher voltage trips the
relay controlled by the driver, and disconnects the grid tie inverter
from the grid.  

I've played with the voltage set points, but the charge voltage
on the Magnum would be too low for good battery maintenance.  If these
were liquid electrolyte batteries, I'd crank up the voltage on the relay
driver.  Since they are AGM batteries, it doesn't seem like a good idea
to do that. 

The work around for this at present is to; 

*   Charge batteries at night in the winter 
*   No problem is expected in the summer 

The batteries are in an insulated box in a shed connected to the
house. The inside of the battery box has a screened hole that is
supposed to allow heated air into the box.  This vent doesn't keep the
batteries warm enough to prevent the problem. 

Is there a temperature sensitive, voltage controlled relay or
diver available?  Has anyone used a temperature bulb with the relay
driver in a way that could solve this problem? Has anyone else come up
against this issue, and if so, what was your solution?

Thanks,

Drake 


Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV Installer
740-448-7328
http://athens-electric.com/ 





___
List sponsored by Home Power magazine
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out participant bios:
www.members.re-wrenches.org
 

 

<>___
List s

Re: [RE-wrenches] AC Coupled Magnum Issue

2013-03-07 Thread Brian Faley
Yes Larry. We are.

 

 

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher,Starlight Solar Power Systems
Sent: Thursday, March 07, 2013 3:36 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupled Magnum Issue

 

ANDyou are still working on that stand-alone, programable,
temperature compensated battery chargerright???


Thank you,


Larry Crutcher

Starlight Solar Power Systems





 

On Mar 7, 2013, at 4:07 PM, Brian Faley wrote:





Hi Allan,

 

In answer to your question: Yes, we're developing an AC side 4kW
diversion mode controller which allows temperature compensated three
stage charging for AC coupled inverter applications.  It is currently in
beta site testing.  

 

Brian Faley

Chief Engineer

Magnum Energy Inc.

2211 West Casino Rd

Everett, WA 98204

Ph 425-353-8833

www.magnumenergy.com

 

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org